    What's wrong with this system?

    TPCo Compressor M# AJB7465AXD
    Bohn Coil M# ADT0700F
    Charged with R-414B
    83 degree ambient
    60 degree walkin box temp

    245 VAC at disconnect
    Both legs 124 VAC to ground
    Common to Run Terms 245 VAC
    Common to Start terms 272 VAC
    Run to Start terms 355 VAC
    Compressor draws 8.05 amps

    Condenser EAT - 82
    Condenser LAT - 102
    Liquid pressure - 190
    Suction pressure - 27
    Liquid line temp - 106
    Suction line temp - 75
    Discharge line temp - 174
    Evap EAT - 61
    Evap LAT - 58

    Customer calls: Box was 38 degrees all week. 7:00A this morning it was 38 degrees. 9:00A this morning is was 55.

    Get there; box is 75 inside. Nothing on the condensing unit is running. Compressor is warm to the touch. Power to the disconnect. Switch off the disconnect. Pull doghouse and compressor terminal cover. Switch on disconnect. Power to ground - all three terminals. Zero volts across common and run. Pull the compressor controls cover. Unit starts. No wires are loose or burnt. Cycle unit several time with disconnect. Always starts and runs.

    What was the problem?

    What are the problems?
    PHM

  2. #2
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    5,176
    Quote Originally Posted by Poodle Head Mikey View Post

    What was the problem?
    Is this a trick question?
    Ok I'll guess It was a dirty condenser unit over heated opened overload customer cleans the coil waiting for you in panic mode. But why was your cond. fan off (controls/wiring)?

  3. #3
    Join Date
    Dec 2004
    Posts
    484
    what does EAT and LAT stand for?

  4. #4
    Join Date
    Sep 2002
    Posts
    9,546

    not a trick question -

    I could not simulate the 'does not run' problem on-site. So I have no definitive idea what it was.

    Nothing at the condensing unit running - sounds like the box stat stuck open. No idea why taking the controls cover off the compressor on the roof would close a stat down in the box. And a stat which had (if that was the problem) been open all day long despite the door being slammed, product moved in and out, etc.

    Condenser is not dirty. Big steel fin spacing, clean, good air flow.

    I do suspect that it is not the correct compressor for the condensing unit. Just my spider-sense tingling though - as I can't read the tag on the CU base plate.

    I am curious if the amp draw is too high. "7465" - is that 6500 BTU's ? At medium temp that would be about 3/4 HP. 6 amps per HP at 240 volts makes it seem a bit high. But the O/L never opened while I was there and if it had been off on the O/L to start with - the condenser fan would have been running.

    NO! Pressure control! The fan wouldn't run without the compressor ruuning as the head pressure would be too low to close the control.

    But the compressor shell was warm - not hot to the touch.

    I have been working on my kitchen, chasing the little woman around, and drinking beer on my breaks all day today - so working on this walk-in was way down on My List by the time he called. But . . . what can you do? I went.

    Hell; I had to go out to Home Depot anyway. May as well fund the trip. <g>
    PHM

  5. #5
    Join Date
    Aug 2002
    Location
    Orange County CA
    Posts
    1,084
    Entering air temp/leaving air temp

    A.C. talk

  6. #6
    Join Date
    Sep 2002
    Posts
    9,546

    Entering Air Temperature - Leaving Air Temperaure

    Sorry about that. It's how my start-up sheets are labeled.
    PHM

  7. #7
    Join Date
    Nov 2005
    Location
    Haymarket VA
    Posts
    642
    Quote Originally Posted by Poodle Head Mikey View Post
    TPCo Compressor M# AJB7465AXD
    Bohn Coil M# ADT0700F
    Charged with R-414B
    83 degree ambient
    60 degree walkin box temp

    245 VAC at disconnect
    Both legs 124 VAC to ground
    Common to Run Terms 245 VAC
    Common to Start terms 272 VAC
    Run to Start terms 355 VAC
    Compressor draws 8.05 amps

    Condenser EAT - 82
    Condenser LAT - 102
    Liquid pressure - 190
    Suction pressure - 27
    Liquid line temp - 106
    Suction line temp - 75
    Discharge line temp - 174
    Evap EAT - 61
    Evap LAT - 58

    Customer calls: Box was 38 degrees all week. 7:00A this morning it was 38 degrees. 9:00A this morning is was 55.

    Get there; box is 75 inside. Nothing on the condensing unit is running. Compressor is warm to the touch. Power to the disconnect. Switch off the disconnect. Pull doghouse and compressor terminal cover. Switch on disconnect. Power to ground - all three terminals. Zero volts across common and run. Pull the compressor controls cover. Unit starts. No wires are loose or burnt. Cycle unit several time with disconnect. Always starts and runs.

    What was the problem?

    What are the problems?
    condensing temp is 120
    SC 14 deg you got juice
    condensor split ltl high 38 deg
    evap temp around 31 DEG
    45 deg superheat what is your evap superheat if you can post you will find problem
    sound like your under feed ,check txv ,due to coil td is 28 deg
    if you got 60 deg box pulling down from long time high superheat high td will
    go towards txv refrigeration problem not elec

  8. #8
    Join Date
    Sep 2002
    Posts
    9,546

    Sarpanch -

    Condenser delta is 20 not 38. I still think that 20 is a bit high for a clean open condenser but it's not 38. <g>

    Looks like the SSH is 45 - but the box just started and was still at 61 degrees too.

    OK, but if it's a "txv / refrigeration problem not elec" then way wasn't the condensing unit running? Cycling on the compressor O/L you think ?
    PHM

  9. #9
    Join Date
    Nov 2005
    Location
    Haymarket VA
    Posts
    642
    well EAT is 82 according to tecumseh pt chart 190 psig 124 deg condensing temp how come conensor split 20 deg how do you measure condensor split 124 - 82 =42 deg condensor split

  10. #10
    Join Date
    Nov 2005
    Location
    Haymarket VA
    Posts
    642
    you don,t measure LAT ? to check condensor spilt
    here is some info i got may help you
    Page 2 Chapter 5 Notes

    Talking about efficiency, the more efficient A/C condensers have a 20, or lower, condensing split than the old standard 30. In the example of the 95 ambient with the clean condenser, the difference in the head pressure would be (95 + 30 = 125 condensing at 281#) – (95+30=115 at 245#) 36# and the difference in the liquid temperature would be (125 - 115) 10.
    Condensing split is the temperature difference between the ambient temperature and the temperature at which the hot discharge gas will condense. Thirty (30) is average for standard A/C units and refrigeration units. High efficiency units are dropping that to 20 and sometimes as low as 10 by increasing the size of the condenser, more fins per inch, and condenser fan capacities to move more air across the condenser surface.

    SUPERHEAT is the difference in the temperature between the vapor in the low side and the temperature at the sensing bulb. The “average” superheat is 10.
    If there is no superheat (0) than the TXV is “flooding.” Note: anything below 5&#176; is low superheat.
    If there is too much superheat (above 20) the TXV is “starving.”
    NOTE: SUPERHEAT IS TAKEN ONLY AT DESIGN TEMPERATURE (preferable just before the thermostat cycles the unit off). Design temperature is what it is rated at. For instance, A/C is designed to provide about a 75 space temperature, medium temperature applications would be 35 to 40 box temperature, and freezers are normally 0 to –10.
    Last edited by sarpanch2001; 09-22-2007 at 11:05 PM. Reason: add

  11. #11
    Join Date
    Nov 2005
    Location
    Haymarket VA
    Posts
    642
    here some more info on condensor split may help you in feature
    Page 2 Chapter 5 Notes

    Talking about efficiency, the more efficient A/C condensers have a 20, or lower, condensing split than the old standard 30. In the example of the 95 ambient with the clean condenser, the difference in the head pressure would be (95 + 30 = 125 condensing at 281#) – (95+30=115 at 245#) 36# and the difference in the liquid temperature would be (125 - 115) 10.
    Condensing split is the temperature difference between the ambient temperature and the temperature at which the hot discharge gas will condense. Thirty (30) is average for standard A/C units and refrigeration units. High efficiency units are dropping that to 20 and sometimes as low as 10 by increasing the size of the condenser, more fins per inch, and condenser fan capacities to move more air across the condenser surface.

    SUPERHEAT is the difference in the temperature between the vapor in the low side and the temperature at the sensing bulb. The “average” superheat is 10.
    If there is no superheat (0) than the TXV is “flooding.” Note: anything below 5° is low superheat.
    If there is too much superheat (above 20) the TXV is “starving.”
    NOTE: SUPERHEAT IS TAKEN ONLY AT DESIGN TEMPERATURE (preferable just before the thermostat cycles the unit off). Design temperature is what it is rated at. For instance, A/C is designed to provide about a 75 space temperature, medium temperature applications would be 35 to 40 box temperature, and freezers are normally 0 to –10.
    don,t take me wrong i am just trying to help you if think im wrong just ignor it

  12. #12
    Join Date
    Sep 2002
    Posts
    9,546

    Condenser split is an air temperature rise comparison -

    Entering condenser - 82

    Leaving condenser -102

    difference - 20
    PHM

  13. #13
    Join Date
    Nov 2005
    Location
    Haymarket VA
    Posts
    642
    come on dude info i just post that is from book