Results 27 to 39 of 46
Thread: 6 Ton Trane
  1. #27
    Jun 2007
    Greenville,North Carolina
    Nice,neat install.Next time check for dryer inside though.Really looks good.
  2. #28
    Sep 2006
    Winter Springs, Fl
    Okay, I'm confused now. So if there are two filter driers it won't hurt the system? I'm sure this happens many times, doesn't it? If someone could clarify the potential issues with this and whether or not it will harm it that would be great.
    In my early days of doing installs ( i've been in for 6 years ) I would install a drier on the liq. line all the time and have never had any callbacks for this extra item. I did it not knowing that the factory installed one already or I would peek into the unit and not see one and assume that it needed one. I learned later that on most equipment now it's not needed. As I stated before, it is not the best way but it will not cause any detrimental harm to the system IMO.
    cobitech:
    On the trane CU's you cannot see the drier by peeking down in through the top. They are mounted outside of the condenser coil on the side behind the quik access panel to the left of the control box. It's the only panel that has two screws along the vertical edge. When you remove them the access panel easily swings open and is removed. On the heatpump models the reversing valve is located here as well. Their mounting location is what used to fool me too. I thought all manufacturers put the guts to the system inside next to the compressor until I looked closer one day and saw the drier. It had a directonal arrow ink printed on the side of it. Oops. live and learn I guess.
    If you can't learn to do something well, learn to enjoy doing it poorly.
    VETO PRO PAC - The Official Tool Bag of HVAC-Talk.com
  3. #29
    OrlandoTech,
    You are absolutely right! It does indeed have a copper spun liquid line drier going vertically inside the cover.
    It is in series with the one that I installed, but I don't see pumping the unit down and recovering refrigerant unless it is adversley effecting the operation of the unit.
  4. #30
    Sep 2006
    Winter Springs, Fl
    Quote Originally Posted by cobitech View Post
    OrlandoTech,
    Glad you found it. It won't affect the initial operation of the unit but over time it could fool a tech if the factory drier plugs up since the restriction would be downstream of the service port and he doesn't think to check for it. This is why it's a bad idea plus like someone else said you an get a slight pressure drop in the system from the extra drier and the added refrigerant you need to use to charge up the system.
  5. #31
    Oct 2009
    i have a trane AC UNIT. its a heat pump model built 10-2006,
    model number 2TWA0072A3000AB. i'm told its a 6 ton unit. long story, but i bought this thing for my house and then found out i can't use it because its a 3 phase unit. i paid 1000 for this thing. i've since bought a rooftop package unit for my house, but don't know what to do with this unit. its never been turned on. i've had people come and look at it and they checked the triggers to see if its ever been turned on and they showed me that the electricity has never been applied. any help here would be a blessing. thanks
  6. #32
    Sep 2006
    Winter Springs, Fl
    Quote Originally Posted by eo1scw View Post
    Well sorry to hear that. You might have a hard time getting all of your money back out of it. If it were me I would go around to some of your local A/C shops that advertise that they do commercial work and see if they would be interested in buying it. Take some good photos of the unit and as much model and serial info as you can to help you sell it. As long as it has never been installed, you stand a better chance of recovering more of your money than if it was installed previously. Good Luck!
  7. #33
    Dec 2003
    An extra dryer is not a problem. Nice job.
  8. #34
    Jun 2009
    Lawng Eyeland
    Thumbs up
    copper spun driers don't have enough dessicant in them to be true driers. More of a prefilter. Shouldn't be a problem as long as you pulled a good vacuum on it. Trane does usually allow suction oil traps anymore. The increased suction velocities due to higher compression ratio compressors makes it not needed. Nice job.
    MK
  9. #35
    Northern Indiana
    Hmm
    Ive been installing Trane equipment since 1992 and I never knew they had a 6ton split cooling unit. I learn everyday. Great looking work. What size lineset does that require? 1 1/8th inch I'm guessing.
  10. #36
    Sep 2006
    Winter Springs, Fl
    Quote Originally Posted by daytonafan View Post
    Yeah I don't know exactly how big they go in split design but I've worked on a Carrier 20ton split before. The 6ton is 3-phase and needs 1 1/8" suction and has the same cabinet design as the residential units. 7.5 ton and up have the commercial grade cabinets.
  11. #37
    Jun 2000
    B.C. Canada
    I do not agree about the quality of the installation, the liquid tight isn't strapped down, there is no inverted trap to ensure the oil stays in the unit and not free drain down into the evaporator coil, the liquid line looks crooked and the sight glass is before the drier. Also it's recommended these days to put the drier close to the metering device as possible. On my job site that would be a fail. Plus I keep looking at that disconnect floating out there. I would have secured it to the unit, probably would have put something new and smaller on.
    One last thing sounds like you are on compressor number 3 or 4? Just my cents, sorry if I broke any of your forum rules.
  12. #38
    Dec 2003
    Quote Originally Posted by Juleous View Post
    An inverted trap on the liquid line would serve no purpose.
  13. #39
    wi
    I like to see the filter after the sight glass also