    Standing Water in Drain Pan

    There is about 1/4 inch standing water in the drain pan for the coil in a Goodman 10 seer air handler. Is this too much water? The pipe that it drains into does not seem to be clogged. Just had this system installed and works great otherwise.

  2. #2
    Join Date
    Feb 2004
    Location
    SC
    Posts
    20,677
    If you're talking about the secondary (or drip) pan, I would think so. The small amount of moisture that might accumulate in the drip pan should evaporate pretty quickly rather than accumulate. Given that, you may have a clogged primary drain.
    No reserve. No retreat. No regrets.

    For those who have fought for it, freedom has a sweetness the protected will never know.

    http://www.airwarvietnam.com/16thSOSGunners2.jpg

    Proud member of KA Club

  3. #3
    Join Date
    Jan 2007
    Posts
    49
    Quote Originally Posted by bootlen View Post
    If you're talking about the secondary (or drip) pan, I would think so. The small amount of moisture that might accumulate in the drip pan should evaporate pretty quickly rather than accumulate. Given that, you may have a clogged primary drain.
    I just noticed that the air handler is not level. In fact it is tilted away from the drain hole and the drain hole is not completely flush with the bottom of the pan. This seems like a contributing factor. Should the air handler be perfectly level and the drain hole flush with the bottom of the pan?

  4. #4
    Join Date
    Sep 2001
    Location
    angola indiana
    Posts
    528
    yes

  5. #5
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    did you install this unit yourself?

    if not and it was just installed, call the company that installed it ask the specific questions

    after you ask them, tell us what they said, is this a horizontal application and

    if its a horizontal, i disagree with one of the answers that was posted here!



    .



    .

  6. #6
    Join Date
    Jan 2007
    Posts
    49
    Quote Originally Posted by Airmechanical View Post
    did you install this unit yourself?

    if not and it was just installed, call the company that installed it ask the specific questions

    after you ask them, tell us what they said, is this a horizontal application and

    if its a horizontal, i disagree with one of the answers that was posted here!
    .
    I did not install myself and the unit is vertical. Tech was just here and will return with shims to set unit level next week. When he tipped unit toward drain hole all water drained out. Coil was rusted right up to the water line. The unit is only a month old, I guess it was born to rust. Tech really did not admit to anything being wrong but says he is doing this for customer satisfaction. Common sense just tells me that there should be no standing water in the drain pan and the rust on the brand new coil proves that point. Your thoughts and comments are appreciated.

  7. #7
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by Physoft View Post
    I did not install myself and the unit is vertical. Tech was just here and will return with shims to set unit level next week. When he tipped unit toward drain hole all water drained out. Coil was rusted right up to the water line. The unit is only a month old, I guess it was born to rust. (Tech really did not admit to anything being wrong but says he is doing this for customer satisfaction.) Common sense just tells me that there should be no standing water in the drain pan and the rust on the brand new coil proves that point. Your thoughts and comments are appreciated.
    your common sense sounds like good old common sense to me



    .

  8. #8
    Join Date
    Apr 2003
    Location
    the Great Pacific Northwest
    Posts
    607
    Many installation instructions and good practice say the indoor coil should be installed with the coil pitched so the condensate drain connection is at a low point. An additional benefit to the pan completely draining it stops the condensate from re-evaporating into the air stream.

  9. #9
    Join Date
    Jan 2007
    Posts
    49
    Quote Originally Posted by hvac-tech-lane View Post
    Many installation instructions and good practice say the indoor coil should be installed with the coil pitched so the condensate drain connection is at a low point. An additional benefit to the pan completely draining it stops the condensate from re-evaporating into the air stream.
    You are correct, I read the installation instructions. This will also create other problems. Pitching the unit toward the drain hole (with shims?) will create a gap(s) under the unit and allow air to flow directly into the coil instead of through the air intake and filter. What is the best way to cover or seal these gaps?
    The air handler sits in a closet with very little clearance around the back of the unit from the inside. Almost impossible to get around back to seal gaps. Is there any other way to get the drain pan to drain properly? Should I pull the coil out and clean the rust off? Once the coil is clean is there some type of spray insulation or rust inhibitor that would prevent rust and condensation that I could spray on the coil? With the coil out it would be easier to seal the back and sides of the unit. Is there a special type of gasket or shim that should be used for this application? What's the right way to do this job?

  10. #10
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by Physoft View Post
    Is there any other way to get the drain pan to drain properly? Should I pull the coil out and clean the rust off? Once the coil is clean is there some type of spray insulation or rust inhibitor that would prevent rust and condensation that I could spray on the coil? With the coil out it would be easier to seal the back and sides of the unit. Is there a special type of gasket or shim that should be used for this application? What's the right way to do this job?
    i am not saying the installer improperly installed anything but;

    if my new unit was rusting after a month due to an improper installation,

    i might have issues with the installer!

    normally, i install all vertical airhandlers level,

    which from what i have noticed (after 27 years) has never caused

    any type of premature rusting, if your that worried about the rust, call the manufacturer and see

    what they suggest, otherwise the tampering that you are thinking about doing, may void your warranty



    .

  11. #11
    Join Date
    Jan 2007
    Posts
    49
    Quote Originally Posted by Airmechanical View Post
    i am not saying the installer improperly installed anything but;

    if my new unit was rusting after a month due to an improper installation,

    i might have issues with the installer!

    normally, i install all vertical airhandlers level,

    which from what i have noticed (after 27 years) has never caused

    any type of premature rusting, if your that worried about the rust, call the manufacturer and see

    what they suggest, otherwise the tampering that you are thinking about doing, may void your warranty
    .
    I called Goodman and they do not offer any kind of spray on rust inhibitor. I do want to risk voiding the warranty so I will leave well enough alone. They did suggust replacing the coil under warranty if it is rusted.

    The unit came with two drain pans one vertical and another pan at 90 degrees tucked in under and along side the verticle pan for horizonital installs. The horizontal pan has legs on the opposite side of the drain which would pitch the whole pan toward the drain hole even if the air handler was not level. I do not see any legs on the vertical pan. It just sits flat, so in order the get this pan to drain properly the whole air handler will have to be pitched toward the drain as suggested in previous posts and in the installation manual. Could the horizonital pan be used instead of the pan that now sits under the coil? It looks to be about the same size. Goodman was silent on this quesiton other than to say that the horzonital pan should have been removed for vertical installs. If that pan can be used it will save a lot of shimming and patching of gaps under the air handler to get it pitched properly.

  12. #12
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by Physoft View Post
    I called Goodman and they do not offer any kind of spray on rust inhibitor. I do want to risk voiding the warranty so I will leave well enough alone. They did suggust replacing the coil under warranty if it is rusted.

    The unit came with two drain pans one vertical and another pan at 90 degrees tucked in under and along side the verticle pan for horizonital installs. The horizontal pan has legs on the opposite side of the drain which would pitch the whole pan toward the drain hole even if the air handler was not level. I do not see any legs on the vertical pan. It just sits flat, so in order the get this pan to drain properly the whole air handler will have to be pitched toward the drain as suggested in previous posts and in the installation manual. Could the horizonital pan be used instead of the pan that now sits under the coil? It looks to be about the same size. Goodman was silent on this quesiton other than to say that the horzonital pan should have been removed for vertical installs. If that pan can be used it will save a lot of shimming and patching of gaps under the air handler to get it pitched properly.

    there you have it straight from the manufacturers mouth, what other questions are there

    they said the horizontal pan should be removed, i remove them on all vertical installs

    now your saying you want to rig something with something that is not supposed to be there

    heck the system is only a month old, usually on installs, everyone gets a 1 year labor warranty

    if your gonna worry about it, dont rig something, ask your installer to do the job properly

    maybe he thinks its a perfect install, what he thinks is yet to be determined



    .

  13. #13
    Join Date
    Apr 2003
    Location
    the Great Pacific Northwest
    Posts
    607
    could you post some pics of the install?

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event