    What can you guys tell me about a Honeywell XC5010C CPU LON Module? Can I program this to output network variables? Would this be done through CARE? Has anyone interfaced to this device before? Tks.

  2. #2
    Join Date
    Nov 2005
    Posts
    93
    "512 NVs supported for LONWORKS integration"
    You can create them with CARE.
    Works OK in LON.
    As for all freely programmable CPU-s, if you changes LON NV-s (and it means XIF changes) after binging, all bindings must be redone.

  3. #3
    Join Date
    Aug 2006
    Location
    New England
    Posts
    520
    Most of what I know of XC5010Cs was not LON based, but I have done a couple of LON jobs with them. The logic is programmable only in CARE (as far as I know), but bindings are like anything else. Like the man says, 512 NVs and freely programmable as long as you have CARE (a quirky, but workable programming environment).

  4. #4
    Join Date
    May 2006
    Posts
    104
    Quote Originally Posted by CtrlF View Post
    What can you guys tell me about a Honeywell XC5010C CPU LON Module? Can I program this to output network variables? Would this be done through CARE? Has anyone interfaced to this device before? Tks.
    Needs to be done with Care 7.0
    If it aint broke dont fix it!

  5. #5
    Join Date
    Aug 2006
    Location
    New England
    Posts
    520
    Quote Originally Posted by reissman View Post
    Needs to be done with Care 7.0
    Or CARE 5.x.

  6. #6
    Join Date
    Nov 2005
    Posts
    93
    or CARE 3.x.x and CARE 4.x.x, if you have.