What can you guys tell me about a Honeywell XC5010C CPU LON Module? Can I program this to output network variables? Would this be done through CARE? Has anyone interfaced to this device before? Tks.
-
09-12-2007, 04:56 AM #2
Professional Member
- Join Date
- Nov 2005
- Posts
- 93
"512 NVs supported for LONWORKS integration"
You can create them with CARE.
Works OK in LON.
As for all freely programmable CPU-s, if you changes LON NV-s (and it means XIF changes) after binging, all bindings must be redone.
-
09-12-2007, 08:26 PM #3
Professional Member
- Join Date
- Aug 2006
- Location
- New England
- Posts
- 517
Most of what I know of XC5010Cs was not LON based, but I have done a couple of LON jobs with them. The logic is programmable only in CARE (as far as I know), but bindings are like anything else. Like the man says, 512 NVs and freely programmable as long as you have CARE (a quirky, but workable programming environment).
-
10-11-2007, 10:38 AM #4
Professional Member
- Join Date
- May 2006
- Posts
- 104
-
10-11-2007, 07:14 PM #5
Professional Member
- Join Date
- Aug 2006
- Location
- New England
- Posts
- 517
-
10-16-2007, 12:08 PM #6
Professional Member
- Join Date
- Nov 2005
- Posts
- 93
or CARE 3.x.x and CARE 4.x.x, if you have.