    Possible causes of Freon Leak?

    Hello,

    I have an Amana 3 ton unit that is just about 2 years old. A couple of days ago I noticed I no longer am getting cool air from my system.

    I called a technician and he hooked up the gauges and he said I was almost empty on Freon. Obviously he also said this is not normal and there's a problem. He filled it up with I think 4 lbs (yep...that's 4 lbs) of freon. He proceeded to test for possible leaks on the lines. He used soap water to try to see if it was leaking on the joints where the copper was brazed, etc. Nothing. He said pressures were fine after the fill-up, etc.

    He mentioned something about if the lines were in any way compromised (i.e. debris, moisture) then that might be a problem. Well, that rang a bell b/c I know that when I was builing the house we had the condensers in one location and we had to move them. I am pretty sure they just moved it and didn't do any kind of vacuuming of the lines now that I recall.

    I'm wondering if that kind of oversight would cause the unit to lose this much freon.

    The technician said he wanted to install some "side glass" (he explained to me that this is something to install on the line itself to check for moisture etc. in the line to see if it needs to be cleaned out), rebraze some of the shoddy braze work (it's not leaking, but they were shoddy...) etc.

    Otherwise he said he is stumped.

    Does any of this make sense? Can dirty lines cause Freon to disappear like this?

    Thanks!

  2. #2
    Join Date
    Jun 2005
    Location
    Near Chicago, IL
    Posts
    3,315
    No, dirty lines will not cause a refrigerant leak.

    If the system was fine before the condensers were moved, then the problem is most likely related to the work that was done at that time.

    Of course, it is also possible that the leak is a new development.

    Most leaks can be easily found, but maybe not pinpointed exactly, with an electronic sniffer. Common areas are the caps on the service ports the tech connects the gauges to, and the caps on the valves on the unit.

  3. #3
    Join Date
    Aug 2003
    Location
    Lincoln, Nebraska
    Posts
    1,051
    If he is going to go through the trouble of installing a sight glass to check for moisture then he might as well pump it down, replace the dryer and recharge the system and forget the sight glass. When he has it empty he can do a nitrogen check with a little 22 and find the leak and repair at that time. As said above an electronic leak detector should be able to find the leak.

    Good luck
    Its a good Life!

  4. #4
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Quote Originally Posted by m kilgore View Post
    If he is going to go through the trouble of installing a sight glass to check for moisture then he might as well pump it down, replace the dryer and recharge the system and forget the sight glass. When he has it empty he can do a nitrogen check with a little 22 and find the leak and repair at that time. As said above an electronic leak detector should be able to find the leak.

    Good luck
    Yup.....my thoughts exactly
    "The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield

  5. #5
    Join Date
    Nov 2006
    Location
    Oregon
    Posts
    853
    Shop for a better tech. I fail to see how installing a site glass will enable him to find the leak.

    A good tech. will have some likely places to start looking based on his experience and he'll use a combination of methods ranging from electronic sniffer, halide torch, high pressure nitrogen, looking for oil residue, UV dye and of course there's everyon'e favorite (ie Mr. Bubbles). The tech. can deploy any and all of them depending on where the trail leads. If all else fails he may also try the isolation technique.

    It could be as simple as a loose or missing schrader valve caps.

  6. #6
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    The tech probably knows that the loss of refrigerant can only be a leak....... sounds like he is worried about the condition of the refrigerant because he probably heard the no vacuum story also, or he is seeing something on his numbers that makes him wonder. Just a thought.
    ___________________________________________


  7. #7
    Join Date
    Sep 2007
    Location
    North Carolina
    Posts
    48
    I also believe that you should question their abilities.

    Which is a shame because you need someone to find the leak, fix the leak, replace the filter drier, leak test system again using nitrogen and a tracer of R-22 and an electronic leak detector, evacuate properly and recharge.

    dont let them waste your time with the dye.
    no need for a sight glass on a residential system.
    Acid and moisture test kits are available to test the system.
    Moisture is not causing u to loose ref.


    If you do not address this properly it will take years off the life of the system.

    If it is a leak in the equipment it may be covered under warranty.
    If it is a leak in the refrigerant line set then it was (more than likely)left there at install.

    I do like to give people a chance to correct mistakes and maybe you should in this case at least discuss this with the owner of the company.

    But

    If you are correct in saying that they did not do it properly I would advise you not try and chase them for warranty.
    Pay some one else to do it correctly.

    You need this to be done correctly- dont pay to have it done wrong twice

    Its not VooDoo
    Its not Magic
    It is an exact science mixed with a desire to do thing right and a little artistic ability

    Just my opinion. you know what they say about opinions?

  8. #8
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,548
    I'm not going to throw the tech under the bus.....maybe he wants the sight glass for a txv and a moisture indicator,don't know I'm not there.One thing sounds like it's a sure bet....you had a half-a$$ move the condenser. Personally, i'd recover all of the refrigerant, install a new drier, pump it up with nitro, check/fix leaks, recharge with virgin refrigerant. Just me though.
    If everything was always done "by the book"....the book would never change.

  9. #9
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Quote Originally Posted by smokin68 View Post
    I'm not going to throw the tech under the bus.....maybe he wants the sight glass for a txv and a moisture indicator,don't know I'm not there.One thing sounds like it's a sure bet....you had a half-a$$ move the condenser. Personally, i'd recover all of the refrigerant, install a new drier, pump it up with nitro, check/fix leaks, recharge with virgin refrigerant. Just me though.
    Yeah me neither smoke, for all we know he wants to do just as you say and we are getting a bad or partial explanation of a conversation that wasn't really understood.
    ___________________________________________


  10. #10
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    5,168
    Is this the unit in the attic? Maybe a drywall screw through a line?

  11. #11
    Join Date
    Sep 2003
    Location
    Western PA
    Posts
    1,242
    Quote Originally Posted by Wj Stevens View Post
    Yeah me neither smoke, for all we know he wants to do just as you say and we are getting a bad or partial explanation of a conversation that wasn't really understood.
    ditto

  12. #12
    Join Date
    Jul 2006
    Location
    MN
    Posts
    173
    The thing probly takes 5 or more lbs.

    A leak happens cause there is a way for gas to escape.

    An electronic detector will find that leak with the gas in it before recovering much easier in my opinion.

    Your tech sounds like he's doing good, a sight glass can only save time and money down the road. and remove a lot of questions.

    As long as he's opening the system recover all after locating leak, install new drier (evac of course) and new refrigerant as long as a question exists. Or plan on replacing drier again in a few days.

  13. #13
    Join Date
    May 2000
    Location
    Rochester, NY, USA
    Posts
    12,650
    Quote Originally Posted by airon View Post

    Your tech sounds like he's doing good, a sight glass can only save time and money down the road. and remove a lot of questions.
    A site glass on a residential system is nothing but trouble.

    Site glass's tend to be used (by less than knowledgeable Techs) to gage the amount of refrigerant in a system. A LOT of tech's will walk up to a system with a site glass on a 72° day and see "bubbles" and assume the system is low on refrigerant and "fill-r-up" till the bubbles go away. The next day the outdoor air temp goes to 95°, guess what, now the system is over charged.....by a mile.


    Never, ever put a site glass on a residential system, JMHO