Thread: Optibelt for Exhaust fans

  1. #1
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes

    Optibelt for Exhaust fans

    I got a flier from Optibelt Corporation, looks like they cover exhaust fan belts. They claim longer life from their belts in exhaust fan applications. Anyboby had experience with these belts? If their claiams are true, what a time saver for me.

  2. #2
    Join Date
    Aug 2006
    Posts
    28
    Post Likes

    Talking Molded belts

    If your belt size is 47" or above these are the best belts out there. More horsepower and smooth face Not the sawtoothed pulley eaters like X series belts. for large horsepower multi-belt applications they're a once a year change perfect for service contracts. I call them Feburary belts because you change them after evrything slows up a bit.

  3. #3
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    Thread Starter
    The 47" and above belts I have no problems with. Its the stinking A18, A19, A20, 3L220, etc. Work is too cheap to put idlers on them, availible from the O.M. Which would give me a longer, more wear surface, belt. Less radius around the pulley and self tensioning.

  4. #4
    Join Date
    Jun 2005
    Location
    DuPage County, IL
    Posts
    151
    Post Likes
    I knew a guy that knew a guy...really, that worked for Opti-Belt. He gave us a free set of 5V1400 belts. We used them on an Air Handler. Those muthas lasted 3 friggen years of 24/7 operation. Not a single crack. They did thin out a little. We finally changed them out. I hate em. Can't make any money selling these puppies if they don't wear out.
    Figman

  5. #5
    Join Date
    Apr 2004
    Posts
    566
    Post Likes
    I've found that those red belts that are segmented and can be atached to provide a fit for any belt work great in those applications,they last a long time and you just buy several feet of the stuff than match it up on the job.

  6. #6
    Join Date
    Aug 2006
    Posts
    28
    Post Likes

    Thumbs up 47" is the magic number

    47" is the cut off for molded belts if it is less than 47" it is a spliced belt made from a straight corded belt with a splice that wants to find a way to straighten out again (like everyone elses belts) so the point is not much differance on the small stuff.
    ps. beware of homemade belts good for a 2 AM call but not much else!

  7. #7
    Join Date
    Jun 2006
    Posts
    147
    Post Likes

    Goodyear

    I have been using Goodyear PD belts for several years and they have paid for themselves many times over. I had a 45hp fan with 4 v-belts and was changing them almost monthly. This fan was short on air and I changed to the PD belts. The belts don't slip which added effeciency and they run for a couple of years before needing replacement. I would have more of them if they made them longer. The only problem is that they prefer a soft start. I have started them without a VFD and it can be done. I would not use them in an application where the fan stops and starts frequently.

  8. #8
    Join Date
    Mar 2008
    Location
    Greenville, SC
    Posts
    4
    Post Likes

    Optibelt

    Hey ya'll,

    A bit more information on the Optibelt HVAC product from an Optibelt engineer.

    The belts have a special cord and fabric wrap that makes the belts very flexible so they can bend around small pulleys. The cord helps the belts to hold their tension better and also they have a higher temp rating so if they do slip they will last longer.

    We put them on at a fast food chain restaurant's exhaust vents and they have been going strong for 8+ months compared to 1 month for the standard belt life.

  9. #9
    Join Date
    Sep 2012
    Posts
    1
    Post Likes

    Optibelt distributor

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.
    Last edited by jpsmith1cm; 09-06-2012 at 08:32 PM. Reason: non AOP member

  10. #10
    Join Date
    Aug 2006
    Posts
    3,691
    Post Likes
    Thread Starter
    I've been using them almost as long as the original post. Absolutely love them in all sizes. They last so much longer than any other brand of belt, there is no comparison. They rarely crack, which BTW will destroy the bearings if not caught soon enough. One of the other guys here hates them. He "pops" the belts over the pulleys, and has ruined motors and fan bearings.

  11. #11
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    bbacon

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.



Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •