Thread: Performance Testing numbers: Good or Bad

  1. #1
    Join Date
    Jan 2013
    Posts
    12
    Post Likes

    Performance Testing numbers: Good or Bad

    Hello experts,

    My installer finally did the performance test for my unit and here are the numbers:
    Brand: HeatController - Comfort-Aire
    Model: HTV036B1C01JLK - 3-ton
    Type: Water to Air, closed loop 1200' total, antifreeze filled in tubes

    HEATING Mode:
    Voltage: 242
    Water In Temp: 50
    Water Out Temp: 43
    Temp Change: 7

    Pressure In (lbs): 24
    Pressure Out (lbls): 13
    Pressure drop: 11

    Return Air Temp: 68
    Supply Air Temp: 95
    Temp Change 27

    COOLING Mode:
    Voltage: 244
    Water In Temp: 44
    Water Out Temp: 52
    Temp Change: 12

    Pressure In (lbs): 24
    Pressure Out (lbs): 13
    Pressure drop: 11

    Return Air Temp: 66
    Supply Air Temp: 39
    Temp Change 27

    These numbers were collected when HWG is OFF. When HWG is ON, the Water Temp In is 40 and Water Temp Out is 39

    What do these numbers tell us about our system? He wanted to use the Manufacture list Flow Rate (GPM) for the pump but I insisted that he must test it and use that number instead. The pump is manufactured by bdmfginc, model QT Flow Center 2-230QFC.

    Thank you.

  2. #2
    Join Date
    Mar 2007
    Location
    Cedar Rapids, Iowa
    Posts
    126
    Post Likes
    These numbers can't be correct. According to page 16 of the Engineering Design Guide ( http://www.comfort-aire.com/download...age-geothermal ) 5.2 PSI drop through the exchanger equals 9 GPM.
    11PSI drop @ 50* EWT equals about 18 GPM. If the numbers are correct the system is WAY over pumped. I also don't see how 18 GPM can still give you a 7* Delta T. With your numbers...

    18 GPM X 7* Delta T X 485 = 61,110 Btu's Heat of Extraction
    The Spec Guide shows a HE of 31,700 Btu's @ 50* EWT W/9 GPM

    According to the numbers a 7* Delta T W/9 GPM @ 50* EWT would equal 30,555 Btu's, very close to the spec value of 31,700 Btu's

  3. #3
    Join Date
    Jan 2013
    Posts
    12
    Post Likes
    Thread Starter
    Thank you SO MUCH for your reply, Bergy. This is why I came to this site, so many knowledge people here. I know something is NOT right with my system but I don't know what is wrong.

    What is your suggestion that I should look into? Thanks.

  4. #4
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    Was a single gauge and a single thermometer used for the water pressure and temperature measurements? Doing so will eliminate the possibility of gauge/thermometer error causing in incorrect measurement of one the pressures/temperatures that will result in a faulty calculation of pressure drop or temperature change.

  5. #5
    Join Date
    Jan 2013
    Posts
    12
    Post Likes
    Thread Starter
    Quote Originally Posted by Nuclrchiller View Post
    Was a single gauge and a single thermometer used for the water pressure and temperature measurements? Doing so will eliminate the possibility of gauge/thermometer error causing in incorrect measurement of one the pressures/temperatures that will result in a faulty calculation of pressure drop or temperature change.
    The tech used the push-type meter that he pressed it thru the P/T plug (I guess) and measured the water temp/pressure. For air temp he poked 2 holes in the vent-tube and inserted a stripped copper wire that connected to a temp-meter (I guess) to measure that.

    He did NOT measure the flow rate (GPM) because he did not have the tool at that time - will be done tomorrow.

    Thanks.

  6. #6
    Join Date
    Oct 2005
    Location
    Pacific Northwest
    Posts
    2,551
    Post Likes
    How close is the pump to the inlet pressure port?

  7. #7
    Join Date
    Mar 2007
    Location
    Cedar Rapids, Iowa
    Posts
    126
    Post Likes
    If you have a non-pressurized loop there is a "Flow Gauge" that's inserted in the water stream and will visually show the GPM. GPM is derived from the pressure drop through the heat pump according to the Entering Water Temp (EWT). This is true of both pressurized and non-pressurized systems. All of the needed information is in the Spec Guide and the Owners manual.

    Page 16 of the Design Guide...

    Performance Data-HT036_Full Load(2nd Stage)
    9 GPM = 5.2 PSI @1080 CFM Heat of Extraction = 30,800 Btu's @ 1250 CFM HE = 31,700 Btu's

    Page 35 of the Owners Manual...

    Unit Operating Conditions (the HT036 chart)
    50* EWT @ 3 GPM/ ton Water side Delta T 6.4*~8.4* Air side Delta T 24*~30*

    This is the information your service tech needs to be looking at and showing you. If he doesn't know where, or what, this information is... Time for someone that does!

    Bergy

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •