    Siemens has released an update to panel firmware that makes ethernet panels more resistant to "network storms".

    PROBLEM:

    Ethernet Field Panels running Firmware Revision 2.8 Build 1104 or 2.7 Build 1006 may stop communicating on an APOGEE Ethernet ALN after a period of heavy network traffic occurs.

    Some of the known symptoms after the field panel fails to communicate on network are:

    Insight and the rest of the network show the field panel FAILED and the field panel gets disconnected from the network.
    Even after the field panel fails on the network, local node table of the panel may show it is still communicating on the network.
    The field panel may still respond to PING and TELNET commands.
    Typically a coldstart of the controller would be only way to bring it back online.
    YOUR ACTION:



    The solution/patch has been successfully tested at several job sites.



    The permanent solution is incorporated into Firmware Revision 2.8 Build 1105 which will be available on StdApps drive within the next 1-2 weeks.
    Dingman from Iowa~
    "A lie gets halfway around the world before the truth has a chance to get its pants on."
    - Sir Winston Churchill (1874-1965)

    The Dingman's webpage, featuring the Ding_Z

  2. #28
    Join Date
    Jul 2008
    Posts
    5

    FIREWALL

    Check The firewall!! I thinks that the problem was over!

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event