Thread: a/c icing up coil on open display cooler...

  1. #1
    Join Date
    Apr 2006
    Posts
    127
    Post Likes

    a/c icing up coil on open display cooler...

    anybody find this to be a problem is that a/c diffusser is right above open display cooler, this is a federal open type with no defrost except when cut-out pressure is met,a/c blowing around 65 deg. air at system, should this display case be moved or diffusser disconnected or blocked off, any recommendations on getting around this... thanks..
    Never Assume Anything

  2. #2
    Join Date
    Apr 2001
    Posts
    677
    Post Likes
    Quote Originally Posted by freeeze43 View Post
    anybody find this to be a problem is that a/c diffusser is right above open display cooler, this is a federal open type with no defrost except when cut-out pressure is met,a/c blowing around 65 deg. air at system, should this display case be moved or diffusser disconnected or blocked off, any recommendations on getting around this... thanks..
    What refrigerant is in this unit and what are the Low pressure control settings (cut-out & cut-in).

    Jabs

  3. #3
    Join Date
    Jan 2007
    Location
    maine
    Posts
    796
    Post Likes
    the diffuser should be moved, it will blow 55 degree air into the case moving the 30 degree air out.. The case might work fine but will have to work harder for sure..

  4. #4
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    at local wawas in this area (nj) i see the returns right above cases & i always wondered what effect if any it had on either system

  5. #5
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    Never had one ice up because of the duct work but have seen them not getting down to temp. They moved the vent and problem solved.

  6. #6
    Join Date
    Apr 2006
    Posts
    127
    Post Likes
    Thread Starter
    Quote Originally Posted by Jabarco View Post
    What refrigerant is in this unit and what are the Low pressure control settings (cut-out & cut-in).

    Jabs
    r22 with cut out at 64psig and cut in at 35 psig
    Never Assume Anything

  7. #7
    Join Date
    Dec 2004
    Posts
    509
    Post Likes
    Your settings are too low for not having a defrost clock. I cant tell you exactly what you want without knowing what temp your trying to hit. 55/70 is close

  8. #8
    Join Date
    Apr 2001
    Posts
    677
    Post Likes
    Quote Originally Posted by freeeze43 View Post
    r22 with cut out at 64psig and cut in at 35 psig
    The settings you have are a good setting for a walk-in cooler but on an open case with R22 I would use 66 psig as cut-in & 40 psig as cut-out.

    Jabs

  9. #9
    Join Date
    Aug 2006
    Location
    Vancouver , Canada
    Posts
    457
    Post Likes

    Talking Open case concerns

    Quote Originally Posted by freeeze43 View Post
    anybody find this to be a problem is that a/c diffusser is right above open display cooler, this is a federal open type with no defrost except when cut-out pressure is met,a/c blowing around 65 deg. air at system, should this display case be moved or diffusser disconnected or blocked off, any recommendations on getting around this... thanks..
    The air from a diffuser WILL disrupt the invisible air curtain and cause spillage of the cold, dry air from the case - so you make that air up with warmer, more humid air from the HVAC system in the store - two things will happen - iced up case and in the very least, inability to hold temperature/ longer run time.

    Does the case have a seperate air curtain? If so, ensure that portion of it is working properly.

    Years ago, Hussmann used to publish the cases had to be out of any air stream ( that includes ceiling fans ) and the design parameters dictated 75 F DB and 50% RH maximum - food for thought.
    Superheat and subcooling tell it all !

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •