Thread: Distech Free prog problem
-
08-26-2007, 11:26 PM #1
Regular Guest
- Join Date
- Mar 2007
- Posts
- 112
Distech Free prog problem
REM Can someone run this code please and tell me what's wrong with line 23 REM MIXEDAIR_SETPOINT_VARIABLE = MIXEDAIR_SETPOINT_CONSTANT.
REM AHU Control for
REM Control Points List
REM Inputs Outputs
REM 1 SUPPLY_FAN_STATUS SUPPLY_FAN
REM 2 RETURN_FAN_STATUS
REM 3 AFS_FILTER
REM 4 SF_VFD_FLT
REM 5 RF_VFD_FLT
REM 6
REM 7 PRESSURE
REM 8
REM 9 RET_RH
REM 10 RETURN_TP SUPPLY_DRIVE
REM 11 MIXED_AIR_TP VLV_COOL
REM 12 SUPPLY_TP FRESH_AIR_DAMPER
REM Variables and Constants Note: V is for Variable and C is for Constant in names.
VFD_SETPOINT_VARIABLE = VFD_SETPOINT_CONSTANT
MIXEDAIR_SETPOINT_VARIABLE = MIXEDAIR_SETPOINT_CONSTANT
REM Outputs to CO's
SUPPLY_DRIVE = CO1
VLV_COOL = CO2
FRESH_AIR_DAMPER = CO3
REM Inputs
RETURN_FAN_DIG_STATUS = RETURN_FAN_STATUS
SUPPLY_FAN_DIG_STATUS = SUPPLY_FAN_STATUS
REM nvi's
REM TEMP Multipliers
IF ( nviFP_02_OSA_TEMP ) = ECONOMIZER_CONSTANT
THEN VLV_COOL = MIXEDAIR_SETPOINT_CONSTANT
ENDIF
END
-
08-27-2007, 06:22 AM #2
That line of code looks OK, check your spelling in the constant and variable assignments. I'm curious why you are assigning the constant to a variable and not using the constant directly.
This line of code is wrong : IF (nviFP_02_OSA_TEMP ) = ECONOMIZER_CONSTANT
It should look like this : IF ( nviFP_02_OSA_TEMP = ECONOMIZER_CONSTANT)
This is also incorrect in the sense that you cannot use an network variable in the code. You must assign it to a variable first
such as, nviFP_02_OSA_TEMP = OSA_TEMPLast edited by dapper; 08-27-2007 at 06:30 AM.
-
08-27-2007, 10:49 AM #3
Regular Guest
- Join Date
- Mar 2007
- Posts
- 112
Dapper,
Thanks,
I got it fixed.
I am confused as the Free Prog manual does not do a good job of explaining what Variables and Constants are. I though thought that a Constant is where you would place the actual setpoint. I thought that a Variable is what is required for the CO to be able to read the set point. If not then what's the difference?
FYI,
I have read the Free Prog manual back to front at least four times and all it does is tell you how to do Cut, Copy and Paste over and over.
-
08-27-2007, 12:29 PM #4
I use Constants for setpoints as well but the CO can use a constant. The primary difference is that the value of a Variable can be manipulated in the code and the Constant can not be. This is why they are generally used for setpoints. You dont want the code to change the value.
The other difference with Constants is that they cannot be altered from a web interface, only through a network management tool or a Distech EC-Display.
-
08-27-2007, 12:38 PM #5
Regular Guest
- Join Date
- Mar 2007
- Posts
- 112
Are you saying that with something like A JACE, I can change a constant? But without a JACE I can't? If you don't have a JACE then how else can you do it other than using A LONtool like Lonwatcher 3 - which means you don't need any variables because you can get to the constant.
Am I missing something here? I can't get any straight forward answers except from you.
Can you show me an example of when you need the variable and when you don't?
-
08-27-2007, 02:52 PM #6
Professional Member
- Join Date
- Aug 2006
- Location
- New England
- Posts
- 517
Constants can be changed through a web interface, but they are packaged in a string of numbers and you'd need javascript to separate them and reassemble them in an iLON100. I don't use Jaces, so I can't tell you if they can separate out the individual constant values from the UNVTs that contain the values.
As Dapper says, variables can be changed in code, so you can assign a network variable value to the internal variable by writing e.g.:
Internal_Variable = nviNetwork_Variable
so when you give a valid value to nviNetworkVariable, that value gets assigned to the internal variable (usually, you have to add some math to convert to correct values, depending on SNVT type). Also, things like reset setpoints would have to be a variable, not a constant because the value is the result of a calculation. In any case, you can always change a constant by using the plugin.
-
08-27-2007, 02:58 PM #7
Regular Guest
- Join Date
- Mar 2007
- Posts
- 112
So are you saying that an nvi cannot be linked to a constant?
And I just read your post three times. I appreciate the answer, but I feel like it went from English to Japanese, then to Chinese and back to English.
-
08-27-2007, 04:27 PM #8
Regular Guest
- Join Date
- Mar 2007
- Location
- Netherlands
- Posts
- 29
Outtacontrol
It is very easy constants are used for setpoints dead bands which you can use in the code or in the pid controllers. Varaibles are the values that are not fixed but they are for instance the resut of a formula in the code. NVI,s are variable so can use the directly in the code or like them to a variable like OAT= nviOut. dont forget the there is a floating point issue if use a SNVT_temp_P you have to devide the snvt vulue by 10 OAT=nviOUT/10.
To have acces to variables and constants you can use LonDisplay but there is also a snvt called nviModify but then you need a lonmanagment tool wih browser. I use mostly a EC-display and when I use a Ilon 100 I use nvi for setpoints. Don,t forget to put the nvi in persistent. this is in case you lost cooms with the ilon than our last value is still there.
If you have instaaled the plug-in there are samples in C:\LonWorks\import\Distech\FreeProg\Code_Library
Good luck
-
08-27-2007, 05:00 PM #9Why would you want to this? If you want your nvi to be your setpoint then click the persistant check box beside the nvi, now its value is kept through power cycles. This is for the case that your are setting this nvi through lonworks browser style application (not bound). If you are actually binding a value to nvi, then make sure your sending node has a reasonable heart beat like 30sec. and there is no need to use persistant check box, actually you can not use the check box if nvi is bound.So are you saying that an nvi cannot be linked to a constant?
If the above is confusing to you, I am afraid you need to review the user guides again, because it seems you are not quite understanding the core concepts yet.
For everyone's infromation,
Jaces can set all the interval values of free progs.
-
08-27-2007, 06:26 PM #10
Regular Guest
- Join Date
- Mar 2007
- Posts
- 112
Amigo,
I know what persistent is. Start at the beginning of the thread and you'll see where I'm going with this.
-
08-27-2007, 07:09 PM #11
Professional Member
- Join Date
- Aug 2006
- Location
- New England
- Posts
- 517
Correct. The simple answer is that a constant is constant. If you want to change it, open the plugin (or wizard) and change the value. If you want to be able to change a value from someplace other than the plugin (like a user interface), use a variable or network variable or both.
-
08-27-2007, 07:58 PM #12
OK, I'll try an example, Building Occupancy Schedule
Building_Schedule (nvi) - network variable {cannot be used as is in code}
Building_Sched (variable) - variable for above nvi
Supply_Setpoint (variable) - setpoint for CO
Supply_Air_Temp (input) - referrence for CO
Chilled_Water_Valve - output for CO
Occ_Supply_Setpoint (constant) = 55
UnOcc_Supply_Setpoint (constant) = 75
code here:
Building_Sched = Building_Schedule (intitate Building_Sched to nvi value)
If(Building_Sched = ON)
Supply_Setpoint = Occ_Supply_Setpoint (Set Supply_Setpoint to value of Occ constant)
Else
Supply_Setpoint = UnOcc_Supply_Setpoint (Set Supply_Setpoint to value of UnOcc constant)
Endif
Building_Sched is a variable because it will change based on scheduler nvi.
Supply_Air_Setpoint is a variable that will hold the value of the Occ or UnOcc constant when Schedule changes.
Occ_Supply_Setpoint and UnOcc_Supply_Setpoint are constants that should never be changed. Other examples might be Outdoor_Air_Lockout and Economizer_ChangeOver_Setpoint
Hope this helps!