    Loss of Freon When Checking Subcooling Superheat ??

    When a technician is testing the charge level or subcooling or superheat, and is using gauges with hoses that are several feet long, how much Freon is lost from filling up the hoses? Should the technician have a canister of Freon with him to replace what is lost when he completes his system check? Thanks.
    Quick reply to this message Reply  

  2. #2
    Join Date
    Aug 2004
    Location
    Florida, Kentucky, Michigan, Ohio, Arizona, Colorado, Nevada, and Califormia
    Posts
    410
    Post Likes
    If the hoses have low loss fittings like most of ours do, the loss is minimal and would take several thousand "checks" before affecting performance.
    "Surprised ?! If I woke up tomorrow with my head sewn to the carpet, I wouldn't be more surprised."
    Clark Griswold
    Quick reply to this message Reply  

  3. #3
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Post Likes

    Fair question

    With low loss fittings and proper techniques you won't lose enough to make a difference with regular service. Should they put more in just because they hooked up? No. The amount you are talking about is not readily measurable, so all they would do is screw the charge up.
    ___________________________________________

    Quick reply to this message Reply  

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Should he have a jug of gas in the truck yes.

    Should he try to put .25 oz. back in, no. ( presuming low lose fittings )
    Quick reply to this message Reply  

  5. #5
    Join Date
    Nov 2005
    Posts
    1,351
    Post Likes
    Be careful, many of the techs on this site and many in the field use one set of gauges for all residential refrigerant types. Which means they dump the charges on their gauges after each use. If your system is near critical and the tech has 6 foot hoses it could affect system performance.
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
    Quick reply to this message Reply  

  6. #6
    Join Date
    May 2004
    Posts
    14,135
    Post Likes
    Quote Originally Posted by emoney1971 View Post
    Be careful, many of the techs on this site and many in the field use one set of gauges for all residential refrigerant types. Which means they dump the charges on their gauges after each use. If your system is near critical and the tech has 6 foot hoses it could affect system performance.

    (cough)

    Bull****

    Please explain to this group what you mean by "critical charge" on a residential unit and how loosing less than on ounce of refrigerant will matter.
    Quick reply to this message Reply  

  7. #7
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Post Likes
    critical charge .....resi AC....... naahhhhhh

    besides..... most resi guys do not dump the hose charge between calls, they deal primarily with just a few refrigerants and have a set for each.
    ___________________________________________

    Quick reply to this message Reply  

  8. #8
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,427
    Post Likes
    Quote Originally Posted by emoney1971 View Post
    Be careful, many of the techs on this site and many in the field use one set of gauges for all residential refrigerant types. Which means they dump the charges on their gauges after each use. If your system is near critical and the tech has 6 foot hoses it could affect system performance.
    I dump the charge from my hoses after every check. Matter of fact I disconnect from the high side of the equipment first, open the high side of the guage to the crossover and then slowly open the low side of the guage to the crossover. IE: I put what liquid I took out of the system right back in. The only thing thing left in my guage set when im done is whatever gas it'll hold at the pressure of the low side. Anyone ever measured how much that is? Oh........ I run 5' hoses if someone is going to do the measurement.
    Use the biggest hammer you like, pounding a square peg into a round hole does not equal a proper fit.
    Quick reply to this message Reply  

  9. #9
    Join Date
    Sep 2006
    Location
    Southern California
    Posts
    86
    Post Likes
    diminimus
    Quick reply to this message Reply  

  10. #10
    Join Date
    Jul 2001
    Location
    VA
    Posts
    2,801
    Post Likes
    Yeah firecontrol.... I think every good tech does that.... I was just saying that you would not vent the hoses to atmosphere between calls.
    ___________________________________________

    Quick reply to this message Reply  

  11. #11
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    I belive that a 6' hose holds 1 oz of liquid refrigerant
    Quick reply to this message Reply  

  12. #12
    Join Date
    Nov 2005
    Posts
    1,351
    Post Likes
    Relax everyone!!!!

    I said to be careful. I now all you amazing techs out there, like myself, dump your charge back into the system on the low side. Or I have a set of gauges for 410 and 22 with low loss fittings and valves, the best method IMO.

    There are however techs out there who don't and you lose a oz. or 2 every-time they hook up. Over time that adds up, and the last tech to hook up could be the one that drops that charge just enough to make a noticeable difference.

    The odds on this happening are small, so I will back down.
    I was trying to be technical and I will never do it again.
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
    Quick reply to this message Reply  

  13. #13
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    23 grams (3/4 of oz) is what my scales said I hold in my liquid line thats full. Suction or low pressure side didn't show any difference.
    Quick reply to this message Reply  

  14. #14
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,546
    Post Likes
    Quote Originally Posted by firecontrol View Post
    I dump the charge from my hoses after every check. Matter of fact I disconnect from the high side of the equipment first, open the high side of the guage to the crossover and then slowly open the low side of the guage to the crossover. IE: I put what liquid I took out of the system right back in. The only thing thing left in my guage set when im done is whatever gas it'll hold at the pressure of the low side. Anyone ever measured how much that is? Oh........ I run 5' hoses if someone is going to do the measurement.

    I pre-charge my gauge hose set before I hook them up.......




















    yeah,yeah, that's the ticket.

    Actually I don't.
    If everything was always done "by the book"....the book would never change.
    Quick reply to this message Reply  

  15. #15
    Join Date
    Nov 2000
    Location
    Upstate, SC
    Posts
    3,097
    Post Likes
    Only 1 oz or so, huh? I remember reading somewhere that a 6 ft hose held 5 ounces of liquid and the article warned against using the high side gauge unless you had reason to. Have I been mislead all these years on something else???
    Quick reply to this message Reply  

  16. #16
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    I always attach the high side gauge I don't know subcooling otherwise. I will recheck my gauges with the liquid line filled but that was what I got the other day.
    Quick reply to this message Reply  

  17. #17
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by smokin68 View Post
    I pre-charge my gauge hose set before I hook them up.......
    I've done that for a critical charge ice machine using 404A. Learned by doing that they were DEAD serious about that machine being critical charge!

    Wouldn't cross my mind to do it for a resi R22 or 410A system, however. I do isolate the high side and then let the remaining liquid charge in the hose back into the low side. That's just good practice.
    Quick reply to this message Reply  

  18. #18
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    4,021
    Post Likes
    Quote Originally Posted by shophound View Post
    however. I do isolate the high side and then let the remaining liquid charge in the hose back into the low side. That's just good practice.
    Along with the AIR too?
    Quick reply to this message Reply  

  19. #19
    Join Date
    Apr 2007
    Posts
    6,343
    Post Likes
    Air is always purged through the gauges upon hookup.
    Quick reply to this message Reply  

  20. #20
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by GAHomeOwner View Post
    When a technician is testing the charge level or subcooling or superheat, and is using gauges with hoses that are several feet long, how much Freon is lost from filling up the hoses? Should the technician have a canister of Freon with him to replace what is lost when he completes his system check? Thanks.

    O God! how to folks get so bored? I wished I had time to worry about stuff like that,
    heck with my busy life that would be like meditation to me.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill



    Quick reply to this message Reply  

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •