    groaning noise at compressor startup

    Hi,

    I had a 3.5 ton 14 SEER Amana RCE36C2C compressor installed as part of a new system a year ago. At the time, I thought it was kind of loud at startup. It makes a loud groaning noise until it gets up to speed, then runs quietly. I asked the contractor about this and he said it was normal.

    Is it normal for an AC compressor to be noisy at startup? Is this hard on the motor or compressor? Is this something a hard-start capacitor could potentially help?

  2. #2
    Join Date
    Nov 2004
    Location
    Naples, Fla.
    Posts
    1,401
    Post Likes
    Your RCE36 is a nominal 3 ton, not 3.5T, a RCE42 would be a 3.5T

    The RCE series uses scroll compressors & they do make a different sound on start up.

    A hard start kit will reduce wear & tear on the compressor & is required if your unit is matched w/ a TXV coil. The RCE is ONLY rated w/ TXV coils.

    Follow your contractors advice.

  3. #3
    Join Date
    May 2006
    Posts
    59
    Post Likes
    Thread Starter
    Quote Originally Posted by coolguysfl View Post
    Follow your contractors advice.
    My contractor gave me no advice as to the presence/absence of a hard start kit, or it's required installation in my model compressor when matched with the correct TXV coils you mention. Is there anything in particular different about 'TXV' evaporators? The evaporator installed is a Goodman CAPF3636B6AA.

    If the noise is normal, fine. But it certainly can't be helping wear, and if there is an option that would improve this otherwise-quiet compressors operation I would like to look into it.

    If my compressor motor is not equipped with a start capacitor, can I improve start performance and decrease noise by adding one?

  4. #4
    Join Date
    Apr 2001
    Posts
    677
    Post Likes
    Quote Originally Posted by lifespeed View Post
    The evaporator installed is a Goodman CAPF3636B6AA.
    I'd better get my Goodman service truck ready.

    <pic removed>

    Jabs
    Last edited by jrbenny; 08-26-2007 at 05:17 PM.

  5. #5
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,974
    Post Likes
    Twilli thinks all Amana's been groaning since they were bought by Goodman
    No Heat No Cool You need Action Fast

  6. #6
    Join Date
    Nov 2004
    Location
    Naples, Fla.
    Posts
    1,401
    Post Likes
    I'd call the contractor back ----- let HIM validate the coil is an approved match.

    BTW -- with the nomenclature, the F in the coil means Flow-rater, no TXV unless the contractor added it on.

  7. #7
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    the noise you hear at start up may be a hermonic vibration from the compressor witch is common with a scroll compressor. This noise can be escalated it the refrigerant lines are strapped to the beams. If the smaller line is touching the wood or cement the noise can be transmitted to the house and can be in some cases quite loud.

    ask your contractor to check and isulate the lines if possible
    if this is what is causing the loud noise

  8. #8
    Join Date
    May 2006
    Posts
    59
    Post Likes
    Thread Starter
    Quote Originally Posted by coolguysfl View Post
    I'd call the contractor back ----- let HIM validate the coil is an approved match.

    BTW -- with the nomenclature, the F in the coil means Flow-rater, no TXV unless the contractor added it on.
    So the expansion valves are different? Obviously he believed the coils were correct, or he wouldn't have put them in.

    Let me get this straight: you believe that the RCE36 should only be used with a TXV expansion valve, not the flow-rate valve in my evaporator? Is this stated somewhere in the Amana literature? It would be good to have some documentation when speaking with the contractor.

  9. #9
    Join Date
    Sep 2006
    Posts
    41
    Post Likes

    Hmm

    Why do you say you have a 3.5 ton unit the 36 in both numbers match and that is a 3 ton unit .I would check your contract and then talk to the contractor.

  10. #10
    Join Date
    May 2006
    Posts
    59
    Post Likes
    Thread Starter
    Quote Originally Posted by fixhvacr View Post
    Why do you say you have a 3.5 ton unit the 36 in both numbers match and that is a 3 ton unit .I would check your contract and then talk to the contractor.
    The contractor stated he was going to install a 3.5 ton. Apparently he installed a 3 ton.

  11. #11
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Where is indoor coil?

  12. #12
    Join Date
    May 2006
    Posts
    59
    Post Likes
    Thread Starter
    Quote Originally Posted by BaldLoonie View Post
    Where is indoor coil?
    Furnace (Amana AMS95) is in the garage, draws through the side from the house, blows up through the evaporator into the ducts in the attic.

  13. #13
    Join Date
    Aug 2007
    Posts
    2
    Post Likes

    RE: growning sound

    First of all is the reason for the hard start kit is the TXV has a equilizing line that shuts the refrigerant flow off during off cycle. During start up the compressor has to overcome the inercia of the lack of equalization. there for the noise. Requiring the hard start Kit. The kit gives the conpressor the extra boost needed to get the compressor past the hump of locked rotor amps.

    Checking the superheat of the unit would be wise. If liquid is feeding back to the system durring the run cycle. this would also be the symptom that you describe.

    Also take note of your units run time. Does it cool? Does it short cycle?

  14. #14
    Join Date
    May 2006
    Posts
    59
    Post Likes
    Thread Starter
    Quote Originally Posted by lost-art View Post
    First of all is the reason for the hard start kit is the TXV has a equilizing line that shuts the refrigerant flow off during off cycle. During start up the compressor has to overcome the inercia of the lack of equalization. there for the noise. Requiring the hard start Kit. The kit gives the conpressor the extra boost needed to get the compressor past the hump of locked rotor amps.

    Checking the superheat of the unit would be wise. If liquid is feeding back to the system durring the run cycle. this would also be the symptom that you describe.

    Also take note of your units run time. Does it cool? Does it short cycle?
    The compressor runs for 15 - 30 minutes when cooling is required. It cools OK, the ducts are 70's sheetmetal and could be larger. The TXV would be external to the evaporator in the liquid line, right? I don't think it has one. Should it? Would this improve performance?

  15. #15
    Join Date
    Aug 2007
    Location
    South Texas
    Posts
    373
    Post Likes
    Quote Originally Posted by Jabarco View Post
    I'd better get my Goodman service truck ready.


    Jabs
    I'm sorry, but that is just plain funny!

  16. #16
    Join Date
    Aug 2007
    Posts
    2
    Post Likes
    check the back of your thermostat make sure that the hole in the wall is sealed.
    The orafice that is in the unit is okay but will allow refrigerant to migrate during off cycle.
    It does not sound as if your unit is off long enough for the miration to take place durring off time. Could be a problem if you are slugging liquid back durring run time. Is the run of copper for your liquid line longer than 50'? Also how high is your evp coil (indoor coil) in relation to your condenser unit?

  17. #17
    Join Date
    May 2006
    Posts
    59
    Post Likes
    Thread Starter
    Quote Originally Posted by lost-art View Post
    check the back of your thermostat make sure that the hole in the wall is sealed.
    The orafice that is in the unit is okay but will allow refrigerant to migrate during off cycle.
    It does not sound as if your unit is off long enough for the miration to take place durring off time. Could be a problem if you are slugging liquid back durring run time. Is the run of copper for your liquid line longer than 50'? Also how high is your evp coil (indoor coil) in relation to your condenser unit?
    The lines are about 30' long. The evaporator is 6' above ground level, the condensor is at ground level. You think liquid could get to the compressor intake during off time and cause a heavy load when it starts? Isn't there a mechanism to prevent this?

  18. #18
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    The correct charge.
    Perhaps you should have read the instructions before calling.

  19. #19
    Join Date
    Apr 2001
    Posts
    677
    Post Likes
    Quote Originally Posted by lifespeed View Post
    Hi,

    I had a 3.5 ton 14 SEER Amana RCE36C2C compressor installed as part of a new system a year ago. At the time, I thought it was kind of loud at startup. It makes a loud groaning noise until it gets up to speed, then runs quietly. I asked the contractor about this and he said it was normal.

    Is it normal for an AC compressor to be noisy at startup? Is this hard on the motor or compressor? Is this something a hard-start capacitor could potentially help?

    Does the compressor have a factory-installed sound blanket? It's a standard feature for your unit. Read about it at: http://www.djsonline.com/amanarce30specs.pdf

    Jabs

  20. #20
    Join Date
    Oct 2006
    Location
    The Beach
    Posts
    1,025
    Post Likes

    Hmm Noise from Compressor

    Check for that sound blanket, put isolation pads under your outside unit, insulation the small ref. line where ever possible. Make sure the lines are not touching any part of the house. Have a HVAC contractor check the charge. These items will help the tranferring of the noise to the house but you will still get some noise from that Amana unit.
    Blue Fox

Page 1 of 4 1234 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •