DX-9100 Timer Reset Duratiion
Using the GX-9100 I have a Timer and a Comparator
The comparator output initiates the timer
I also have an inverted output from the same comparator connected to
the reset connection on the same timer
This means that either the comparator output (LS1) is initiating the timer(I1@) or
it is reseting the timer(RS1@)
Can the reset signal be a constant signal or does it have to be
a momentary pulse??
Thank you
-
08-22-2007, 01:36 PM #2
Professional Member
- Join Date
- Nov 2005
- Posts
- 919
-
08-22-2007, 10:04 PM #3
Professional Member
- Join Date
- Jun 2001
- Location
- San Diego, CA
- Posts
- 1,146
If held - as if issued by a PLC 'SET' statement the timer will be eternally reset.
If momentary - as if issued by a PLC 'COS' statement it will reset once for each COS.
-
08-24-2007, 05:50 PM #4
Thank you
You were right both ,ways worked good