    Please me to chouse the controller for Modulating Damper

    The modulating actulator (Belimo Model SM24-SR90 )it use singnal control On/Off by Potentiomer 135..140 Ohm..(Pls see attached)MY QUESTION AS BELLOW:
    1. How to control this damper because of i used to use another model that i used sinal 0-10 V to control ON/OF ...
    2.My controller can give singnal 0-10v,4-20 mA,
    3. kindly help me to explain the above mention control gear ( Potentiomet 135..140 Ohm) and where to buy this product
    thank a lot
    ton
    Attached Files Attached Files

  2. #2
    Join Date
    Jun 2007
    Location
    Feasterville, Pa.
    Posts
    43
    The Belimo actuator you are using modulates based on a varying resistance between the signal terminals. We have hooked up many actuators that have this type of input. We always use the RES-1 from Kele. It will accept a 0-10v or 4-20mA signal. See below.

    Good luck!

    res-1e.pdf

  3. #3
    Quote Originally Posted by Tubes110 View Post
    The Belimo actuator you are using modulates based on a varying resistance between the signal terminals. We have hooked up many actuators that have this type of input. We always use the RES-1 from Kele. It will accept a 0-10v or 4-20mA signal. See below.

    Good luck!

    res-1e.pdf
    thank u so much for your replies

  4. #4
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,329
    Wheatstone bridge. Get an actuator that uses you signal. or a converter from KELE which will cast about 250.00

  5. #5
    Join Date
    Jan 2007
    Posts
    735
    Also try ACT - Advanced Control Technologies

    http://www.act-solutions.com/

  6. #6
    Join Date
    Jan 2003
    Location
    USA
    Posts
    1,658
    >Get an actuator that uses you signal. or a converter from KELE which will cast about 250.00

    Swap the actuator if it's that much. That SM has been in service for years, they discontinued that thing many moons ago.

    Nothing I hate more than controls driving, controls driving, controls……….

  7. #7
    Join Date
    Apr 2007
    Location
    little rock ak
    Posts
    143
    try robertshaw controls conert to pneumatic one it will work much better

  8. #8
    Join Date
    Jun 2007
    Location
    Feasterville, Pa.
    Posts
    43
    Why would you want to convert to pneumatic? You would then need to get a pressure transducer, not to mention an air source? Is there some sort of advantage that I am missing?

  9. #9
    Quote Originally Posted by ton_691 View Post
    The modulating actulator (Belimo Model SM24-SR90 )it use singnal control On/Off by Potentiomer 135..140 Ohm..(Pls see attached)MY QUESTION AS BELLOW:
    1. How to control this damper because of i used to use another model that i used sinal 0-10 V to control ON/OF ...
    2.My controller can give singnal 0-10v,4-20 mA,
    3. kindly help me to explain the above mention control gear ( Potentiomet 135..140 Ohm) and where to buy this product
    thank a lot
    ton
    as above mention for Belimo Model SM24-SR90 ,i am confuse abouth the switch between A and B , when i select the switch at the font of acutator to "A" position the actuator will be turn left and when i select "B" actuator will be turn right ,If i need to control by potentio meter, how to set these switch position .

  10. #10
    Tubes110,

    Relax, Rolo's just puttin' you on. He does this all the time just to get a rise out of everyone.

  11. #11
    Join Date
    Sep 2006
    Location
    Rhode Island
    Posts
    244
    "outtacontrol" has to be one of the best HVAC Talk names I have seen on here... Thanks for the chuckle....

  12. #12
    Join Date
    Jan 2003
    Location
    USA
    Posts
    1,658
    as above mention for Belimo Model SM24-SR90 ,i am confuse abouth the switch between A and B , when i select the switch at the font of acutator to "A" position the actuator will be turn left and when i select "B" actuator will be turn right ,If i need to control by potentio meter, how to set these switch position .

    The A-B switch changes the action of the actuator. If its clockwise with no signal with the switch in the A position, the actuator will go full counter clockwise in the B position with no signal. Easier to explain with 0-10v

    A position

    0v = full clockwise
    10v = full counter clockwise

    B position

    0v = full counter clockwise
    10v = full clockwise

    Not sure if I have the CW or CCW right, but you get the point. Set this switch to match your program. Command it open and if it's closed, flip the switch. If it's not moving at all when you change your signal, you have something mucked up or the actuator is dead.

    >try robertshaw controls conert to pneumatic one it will work much better

    LOL there we go.

    Start with 0-10v out of the controller, then get a UPC to convert to pneumatic, pneumatic to 135ohm transducer, finally the actuator. Almost forgot, and an EP to cover the safeties also. Please post the pictures in the wall-o-shame when you’re done.

    Here I thought it was HW's motto "jobs not done till the vans empty". You have this stitched on your shirt also Rolo?

  13. #13
    Thanks Shiff,

    You might actually know me. I did the Plant Physiology job a few years ago with the Argus System.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event