    Any one out there know how to size plates that are solid , size being 24 x 48 they fit down into a ceiling panel grid and were originally used for hot water heating panels and i wanted to use them for freezing panels in a walk in freezer as the shelving parts .I am wondering if this would work,and would this be cost efficient to run as no fans,no defrost other than a manual one.It seems that in a modern day freezer, something is always running driving up operating costs. thanks jeff.Ps. any type of refrigerant excepable and horsepower.

  2. #2
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    Post Likes
    dole plates widely used in freezers, but they are storage freezers. No way you can freeze product with a Dole plate.

  3. #3
    Join Date
    May 2004
    Location
    Mississippi Gulf Coast
    Posts
    56
    Post Likes
    Years ago, we used plate type evaporaters in brine tanks, and ice holds in fishing boats. We sized the compressors @ 8 to 10 square feet of surface area per ton of refrigeration. In your case, you have 8 ft2 of surface, use 1 ton (12000 btu) per plate. As far as refrigerant, I would use 404A. TXV selections should be made using Sporlan's selection liturature. Be sure to protect your compressor with oil separator, and accumulator.

  4. #4
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,164
    Post Likes

  5. #5
    Join Date
    Jul 2007
    Posts
    4
    Post Likes
    Thread Starter
    Id like to thank all that replied , i found info by your web site in dole plate quick plate freeze sizing cant believe i didnt check back sooner , boy time flys.thanks jeff