    eastern north carolina
    Question h20 piping wrong
    customer has about 35 air handling units that are piped backwards, chill
    water goes in on entering air side of the coil, what effect does this have on
    capacity & humidity control? from 5 to 40 hp.
    Dec 2003
    45th Parallel
    10% reduction in capacity comes to mind, but you should probably contact the Sales Engineer that sold the job and ask him. Or ask the Manufact of equip.
    May not be an issue unless coils are marginally sized.
    Ohio
    One effect is a probable reduction in intended dehumidification capability.
    jogas
    Aug 2005
    Turbovac,
    what you are referring to is parallel flow which has a low LMTD, "less effiecient". Additional coil stress, chilled water meets hot air.
    Counter flow, High LMTD cold water meets cold air. Best practice.
    Jesaire
    Jul 2001
    VA
    Quote Originally Posted by turbovac View Post
    Doesnt matter, because it will be blamed for everything forever no matter what....lol Price up a fix.