    superheat and subcooling
    Hi'' guys This is the question'': We have York air cooler liquid chiller model# YCAJ98XV6 RECIPROCATING HERMETIC' The situation is we have 3 in superheat and 6 subcooling' suction 70psi dish 250 to 275 psi set-point 41 but no drop not more than 46deg lwt. all fan good''''''' thanks
    juan clavell santiago
    UTAH
    How's your water treatment? Checked the barrel? Strainer plugged, water pressures normal? EWT?
    have you checked youre glycol % I have seen that if it is higher than specs then you get no heat transfer make sure it is about 30% or if you have specs from the blue prints or original install then use that %.
    If you find it bad 3 different ways- ~its bad~