    OK boyz - here is a question - hope someone can help - - - -
    I have a 3 stage water cooled A/C that has a V48AE-2 * 3 way water valve on the first stage cooling - the bypass port is piped to the common water discharge header. The other 2 systems have V46AE-1 * 2 way water valves that have the condensers dump back into the common water discharge header.
    This is a brand new unit that has the first stage with the bypassing water valve feature to establish there is condenser water flow via a flow switch; if there is water flow, the A/C will run.
    I DO NOT require this ' feature', and even though the bypass line has a ball valve to shut it off, the rest of the valve(s) are piped in tight with no unions or isolation valves. The problem is that the 3 way water valve is bypassing like mad, I have tried everything short of taking it apart, but due to the critical nature of this A/C, don't want to disassemble anything until I have a repair kit on hand ( part # STT17A-617R ) - problem is Johnson tells my wholesalers one is not available for 2 weeks. Repair kits are available for the 2 way valve ( # STT17A-610R ), but they can't tell me if I can get away with the 2 way valve kit to use on the 3 way valve.
    I have over the years done lots with Johnson 2 way valves, and have not had real good luck with taking them apart without having new parts on hand, but am limited on experience with the 3 way valves. If there was room to remove the valves and plop in a new 2 way valve in place of the 3 way valve, I would have done that yesterday, but I mean, it is tight!!
    Finally, my question - If I had the ' innards ' for a V46 valve and a seat repair kit, could I take the bottom ' bypass ' portion off the 3 way valve, bolt on the pressure bellows, and make the 3 way valve a 2 way valve??
    OR, is there a website that gives the blowup of these valves ??
    Thanking you all in advance -
    Dave Beauchesne CM
    Superheat and subcooling tell it all !
    You have a ball valve on the bypass line, shut it..theres your 2 way valve.
    Vancouver , Canada
    Water valve
    I have closed it, it is bypassing like mad in the ' regular ' or calling for cooling mode - like I said, I did everything I could to get it to stop - loosen the spring tension, and take a couple screwdrivers to lift up the plunger off the seat, etc., the thing now maintains 135 psi head on R-22 - there must be something under the seat, as only a few hours earlier, it maintained 225 psi like a dream, with the bypass feature closed off. I have throttled the water supply ( between 80 and 90 psi by the way ) to keep the head pressure up, but I will tear the ball valve on the supply line soon I am afraid.
    My concern is taking it apart without the necessary parts on hand, and when I do get it apart, can it be converted to a 2 way from a 3 way valve by removing the bottom ' block ' ???
    Thanks for the reply--
    Dave B
    Annapolis,MD
    I have seen this problem when the valve is not installed properly[flow]
    Is the valve in the supply or return piping?
    Brooklyn, NY Occupation: HVAC Service Contractor
    You probably have this but maybe not.
    Vancouver , Canada
    Thumbs up Water Valves
    PHIXITMAN - Yes, the arrows are all pointing the correct way, and the valve is in the supply line - - - -
    ROC - Do you have a similar link for the V48 series 3 way regulating valve? - my ineptitude on the computer and the fellow I spoke with at Johnson have stymied my efforts to get any info - the link for the V46 series you sent is great - thank you!!
    Thanks for the help so far - I will follow up when I get this figured out.
    Dave B
    Vancouver , Canada
    Water valves
    ROC - Thanks for the info - parts on order - got 4 days off - will advise on how things go.
    Smile
    Four days off in the summer. Geez what a great job you got. I haven't had a summer vacation in 36 years.
    Vancouver , Canada
    Quote Originally Posted by roc service View Post
    Yeah, my job right now is OK that way - - - but after 28 years in this biz, I still have only had two weeks off in a row ONCE, never more than that - oh well, that is the price you pay.