I have a 3 stage water cooled A/C that has a V48AE-2 * 3 way water valve on the first stage cooling - the bypass port is piped to the common water discharge header. The other 2 systems have V46AE-1 * 2 way water valves that have the condensers dump back into the common water discharge header.
This is a brand new unit that has the first stage with the bypassing water valve feature to establish there is condenser water flow via a flow switch; if there is water flow, the A/C will run.
I DO NOT require this ' feature', and even though the bypass line has a ball valve to shut it off, the rest of the valve(s) are piped in tight with no unions or isolation valves. The problem is that the 3 way water valve is bypassing like mad, I have tried everything short of taking it apart, but due to the critical nature of this A/C, don't want to disassemble anything until I have a repair kit on hand ( part # STT17A-617R ) - problem is Johnson tells my wholesalers one is not available for 2 weeks. Repair kits are available for the 2 way valve ( # STT17A-610R ), but they can't tell me if I can get away with the 2 way valve kit to use on the 3 way valve.
I have over the years done lots with Johnson 2 way valves, and have not had real good luck with taking them apart without having new parts on hand, but am limited on experience with the 3 way valves. If there was room to remove the valves and plop in a new 2 way valve in place of the 3 way valve, I would have done that yesterday, but I mean, it is tight!!
Finally, my question - If I had the ' innards ' for a V46 valve and a seat repair kit, could I take the bottom ' bypass ' portion off the 3 way valve, bolt on the pressure bellows, and make the 3 way valve a 2 way valve??
OR, is there a website that gives the blowup of these valves ??
Thanking you all in advance -
Dave Beauchesne CMSuperheat and subcooling tell it all !
-
08-08-2007, 04:24 PM #2
Member
- Join Date
- Apr 2004
- Posts
- 174
...
You have a ball valve on the bypass line, shut it..theres your 2 way valve.
-
08-08-2007, 05:19 PM #3
Professional Member*
- Join Date
- Aug 2006
- Location
- Vancouver , Canada
- Posts
- 291
Water valve
I have closed it, it is bypassing like mad in the ' regular ' or calling for cooling mode - like I said, I did everything I could to get it to stop - loosen the spring tension, and take a couple screwdrivers to lift up the plunger off the seat, etc., the thing now maintains 135 psi head on R-22 - there must be something under the seat, as only a few hours earlier, it maintained 225 psi like a dream, with the bypass feature closed off. I have throttled the water supply ( between 80 and 90 psi by the way ) to keep the head pressure up, but I will tear the ball valve on the supply line soon I am afraid.
My concern is taking it apart without the necessary parts on hand, and when I do get it apart, can it be converted to a 2 way from a 3 way valve by removing the bottom ' block ' ???
Thanks for the reply--
Dave BSuperheat and subcooling tell it all !
-
08-08-2007, 09:17 PM #4
Professional Member
- Join Date
- Apr 2007
- Location
- Annapolis,MD
- Posts
- 28
I have seen this problem when the valve is not installed properly[flow]
Is the valve in the supply or return piping?
-
08-09-2007, 06:33 AM #5
You probably have this but maybe not.
-
08-09-2007, 09:22 AM #6
Professional Member*
- Join Date
- Aug 2006
- Location
- Vancouver , Canada
- Posts
- 291
Water Valves
PHIXITMAN - Yes, the arrows are all pointing the correct way, and the valve is in the supply line - - - -
ROC - Do you have a similar link for the V48 series 3 way regulating valve? - my ineptitude on the computer and the fellow I spoke with at Johnson have stymied my efforts to get any info - the link for the V46 series you sent is great - thank you!!
Thanks for the help so far - I will follow up when I get this figured out.
Dave BSuperheat and subcooling tell it all !
-
08-09-2007, 03:07 PM #7
-
08-09-2007, 03:22 PM #8
Professional Member*
- Join Date
- Aug 2006
- Location
- Vancouver , Canada
- Posts
- 291
Water valves
ROC - Thanks for the info - parts on order - got 4 days off - will advise on how things go.
Superheat and subcooling tell it all !
-
08-09-2007, 04:08 PM #9
Four days off in the summer. Geez what a great job you got. I haven't had a summer vacation in 36 years.
-
08-09-2007, 04:38 PM #10
Professional Member*
- Join Date
- Aug 2006
- Location
- Vancouver , Canada
- Posts
- 291


Reply With Quote