    question, are all copeland rebuilt compressors shipped with poe automatically nowadays, including high temp applications? i ask this because we have a customer that had a compressor failure about 6 months ago. the customer is a healthcare facility with its own maintenance staff. they changed the compressor themselves. the unit has a low pressure lockout switch, with time delay heater. it will intermittently trip the switch, watched it all day today, no lockouts, good operation. after i left, i wondered if it had poe oil in it, scavenging pipes, and intermittently blocking txv or drier. forgot to check compressor oil, hindsight is 20-20. any thoughts?
    Medford Oregon
    No, but the oil type is part of the model number
    KAJB-0075-IAA-800 5 = mineral oil
    KAJB-007A-IAA-800 A = A/B oil
    KAJB-007E-IAA-800 E = POE
    4DA3R18M0-TSK-800 0 = mineral oil
    4DA3R18ME-TSK-800 E = POE
    3DB3F22K0-TFC-800 0 = mineral oil
    3DB3F22KE-TFC-800 E = POE
    no "A" in Discus (A/B oil)
    this won't apply to a non Copeland rebuilt
    Feb 2007
    Northern NJ
    thanks rocket
    Jan 2006
    DFW Metroplex
    Quote Originally Posted by rocket View Post
    Copeland only makes 7 different models?...............................
    Jan 2006
    DFW Metroplex
    Quote Originally Posted by tjc76 View Post
    If the oil IS scouring the pipes you won't have intermittent txv or drier issues..........you'll flat out plug the hell out of them.
    Medford Oregon
    Copeland makes many models , 7 examples given to show examples of nomenclature on how to identify oil type.
    you were joking right?
    Jan 2006
    DFW Metroplex
    The smiley at the end should have been a dead giveaway, but yeah rocket, I was joking.
    The only thing I see wasn't covered is "L"...........now rocket, don't say anything and lets see if TJC76 knows or has a guess.