chiller
I am on call today and a chiller is down,i have never worked on a chiller before,don't know m\n,s\n or make,what are the basics that i need to look for.
-
08-05-2007, 08:59 AM #2
Professional Member
- Join Date
- Aug 2000
- Location
- USA
- Posts
- 4,935
Waterflows is always the first order of business. Condensor coil clenliness if air cooled. Alot of times its not the chiller it's the ancilary equipment, tower fans off, clogged strainers, dirty coils, etc.
Your poor planning does not constitute an emergency on my part!!!!
-
08-05-2007, 11:15 AM #3
Abs is right. Think simple, think flow. Without flow or lack of flow, work is not being performed adequately. Don't let it overwhelm you, just because it is a chiller system. Look at things abs described first. Good luck.
"Excellence is the gradual result of always striving to do better"
-Pat Riley
-
08-05-2007, 03:32 PM #4
I can't imagine being on duty and running a chiller call without ever having worked on one before. Is there anyone else on duty with you that you can call for help? Maybe a buddy in the HVAC field that can help you out?
-JB
-
08-05-2007, 08:40 PM #5
Professional Member
- Join Date
- Oct 2005
- Location
- Ohio
- Posts
- 41
thanks for they help,didn't have to run the call
-
08-05-2007, 11:44 PM #6
tomorrow, you might want to ask for some chiller time with someone who knows what they are doing so that you can get some experience.
good luck.The weak aren't destroyed by the strong.