    Difference between 80% and 95% gas furnace
    Could someone please explain the difference between an 80% and 95% gas furnace? While I know the difference relating to efficiency, I'm curious how different they are mechanically, such as why doe the 80% can use a regular chimney and the 95 only needs pvc. Does the 80% run that much hotter?
    Also, if the 95 is so much better why would anyone even want the 80%.
    Aug 2012
    North Dakota
    well the 90% plus furnace is known as a condensing furnace (ie more heat is removed until the products of combustion are allowed to reach their due point) thus commanding the pvc venting," Water" containing acid
    As far as why an 80% unit some reasons may be venting issues, though it's generally a $ thing
    Mar 2009
    Mount Holly, NC
    the 90+ furnaces are generally made of stainless steel to survive the acid condensation collecting in points of the furnace.
    dollar for dollar, the 80% equipment can be a better value if you already have the venting in place for it. no modifications are needed for drain provisions, there's no freeze danger if installed in non conditioned space, and they can be quieter. so on a budget, the 80% can be a bargain, with only a small loss in efficiency.
    I generally install 90% equipment, because there are more options with installation, and it's a fuel savings that looks good on the quote.
    The TRUE highest cost system is the system not installed properly...
    Find a HVAC-Talk Contractor by clicking here
    Do you go to a boat repairman with a sinking boat, and tell him to put in a bigger motor when he tells you to fix the holes?
    I am yourmrfixit
    Jan 2012
    Arrowhead Stadium
    90% has a secondary heat exchanger dropping exhaust temp from around 400 to 100 degrees. more heat inside,less outside.
    Apr 2003
    Maple Grove, MN
    With an 80% furnace, 20% of the heat created goes up the flue pipe. This waste heat is still pretty hot, too hot for pvc pipe.
    A higher efficient furnace basically takes your flue pipe and routes it a few more times through the airstream so that more of the heat goes into your home, and less is wasted through your chimney. The problem is that the flue gas actually has a lot of acidic moisture contained in it. As long as it is kept nice and hot, it will be carried out your chimney pipe and won't cause any problems. As the flue gas gets cooler (i.e.. a more efficient furnace), this acidic moisture will begin to condense out of the exhaust gas. That means that the furnace and it's flue pipe need to be designed differently, so that the parts that are in contact with this corrosive acid water will be able to withstand it.
    Cleveland, OH
    About 15%
    Good? Bad? I'm the guy with the gun.
    Statements made by me are strictly my opinions and do not reflect the opinions of my employer. I am not authorized to make any official statements on behalf of my employer.
    Any technical advice offered by me is for educational purposes only, all HVAC related repairs should only be attempted by qualified personnel.
    Jun 2001
    In southern climates and areas with cheap gas rates, payback time may be too long to justify the 95% furnace vs. 80%.