    increse CFM ??

    If I had a 3 ton ac with an ahu that derlivered 1200cfm- would installing a fan that produces 1400-1600cfm improve the amount of cooling being delivered???

  2. #2
    Join Date
    Dec 2003
    Location
    Nevada
    Posts
    1,815
    What symptoms do you have that you are trying to correct? The scenerio you suggest could just make it worse.
    Quote
    “Engineers like to solve problems. If there are no problems handily available, they will create their own." Scott Adams

    "We can't solve problems by using the same kind of thinking we used when we created them."
    Albert Einstein

  3. #3
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    5,987

    Exclamation

    Quote Originally Posted by jmiles View Post
    ... Would installing a fan that produces 1400-1600cfm improve the amount of cooling being delivered ?
    NO !
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  4. #4
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,548
    Quote Originally Posted by jmiles View Post
    If I had a 3 ton ac with an ahu that derlivered 1200cfm- would installing a fan that produces 1400-1600cfm improve the amount of cooling being delivered???
    It would remove less humidity.

    In short, NO.

    400 CFM/ton is about perfect here in Florida.
    If everything was always done "by the book"....the book would never change.

  5. #5
    Join Date
    Sep 2002
    Location
    Boise Idaho
    Posts
    1,032
    no!!! more cfm = air temp would be warmer, less air, air would be colder. The out-put is determined by the comp btu, moving more air will not change that, it will change moisture removal or run the risk of freezing the coil (if you slowed it down)

    matt

  6. #6
    Join Date
    Apr 2001
    Posts
    669
    Yes, more CFM would increase the suction pressure and in turn increase the capacity of the condensing unit. However, that increase in capacity will be an increase in sensible heat and less latent heat which will probably result in less comfort; depending on your geographical area.

    Jabs

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    66,750
    Might, or it might not.

    Depends on the duct system, you might not get more then another 1000 CFM.

    You will lose humidity control if it does move more air.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Apr 2006
    Posts
    101
    400 cfm per ton of cooling, more airflow across the coil will cause the coil to freeze up, you must try to keep a load up on the coil for an efficient system..

  9. #9
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    14,433
    more airflow across the coil will cause the coil to freeze up
    Huh?

    You'd better think about that one.....

  10. #10
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,641
    Quote Originally Posted by freeeze43 View Post
    400 cfm per ton of cooling, more airflow across the coil will cause the coil to freeze up, you must try to keep a load up on the coil for an efficient system..


    hows it do that??

  11. #11
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by smokin68 View Post
    It would remove less humidity.

    delete, i need my reading glasses!



    .
    Last edited by Airmechanical; 07-23-2007 at 10:37 PM.

  12. #12
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by freeeze43 View Post
    more airflow across the coil will cause the coil to freeze up

    can't agree with this either!



    .

  13. #13
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,852
    Less humidity control. Increased air pressure problems. Increased load problems. All around bad idea.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


Page 1 of 3 123 LastLast