    Demand cooling in operating continuously

    I have three 27HP Discus compressors operating most of the time in Demand Cooling mode. Condensing pressures don´t look bad: 180 - 200 psi. I suspected suction filters cartridges plugged, remove them, and there was no change of behavior. I checked the handbook and noted that these compressors are not built with suction inlet mesh screens, so that an obstructed screen is not an issue. Now I am wondering if there could an internal problem within the compressor that might be allowing discharge gas into the suction side, so that the discharge temperatures are higher than expected. What do you think ?

  2. #2
    Join Date
    Jul 2005
    Location
    FLORIDA
    Posts
    1,162
    what is the temp of the suction lines coming into your header
    there is where you will find the answer you seek

    superheat will make your demand cools stay on plus we are in the middle of summer suction lines with poor insulation will hurt also

    also have found some that were jumped out to run always
    sounds like your having fun now

    do you have a sub cooler on this rack and is it working

    there are a host of things that could be driving up your suction gas temp
    so keep looking for them all and good hunting

    what is your rack set to run also, could be its running to low, on an ice cream rack i would run from 7-11psi any lower and not reaching temp and i am looking for a reason
    once you think you've seen it all
    (THINK AGAIN)
    I would rather work for free than be look upon as a thief!!!!!

  3. #3
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347

    *

    Quote Originally Posted by rackrookie View Post
    I have three 27HP Discus compressors operating most of the time in Demand Cooling mode. Condensing pressures don´t look bad: 180 - 200 psi. I suspected suction filters cartridges plugged, remove them, and there was no change of behavior. I checked the handbook and noted that these compressors are not built with suction inlet mesh screens, so that an obstructed screen is not an issue. Now I am wondering if there could an internal problem within the compressor that might be allowing discharge gas into the suction side, so that the discharge temperatures are higher than expected. What do you think ?
    it would be a craps shot without much more info! (need more information)



    .

  4. #4
    Join Date
    Mar 2005
    Posts
    202
    Check your discharge line temp. You may find out that you have a faulty sensor or module.

  5. #5
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Quote Originally Posted by dirtyboy103us View Post
    what is the temp of the suction lines coming into your header
    there is where you will find the answer you seek
    Wise words - Not much more to add here.

  6. #6
    Join Date
    Jul 2005
    Location
    FLORIDA
    Posts
    1,162
    Quote Originally Posted by markettech View Post
    Wise words - Not much more to add here.


    bullshiet





    you could add to it if you wanted to, i know it, now your holding back,
    you got way to many miles on you to lay low and its killing the young guys

    guys like you, jwc,dow and ice and a whole host of guys here love to teach and work on the side of young guys and see the lights turn on as they learn



    i had my grandson on a winn dixie roof when he was three so i know where your at, hang in there , and he loved it also
    Last edited by dirtyboy103us; 07-22-2007 at 04:33 PM.
    once you think you've seen it all
    (THINK AGAIN)
    I would rather work for free than be look upon as a thief!!!!!

  7. #7
    Join Date
    Jun 2004
    Posts
    182
    One simple question here, "Do you have frost on your suction line?" If your suction line is not frosted your suction line superheat is too high. Answer this if you can and I'll try to get back and explain when I get more time.

  8. #8
    Join Date
    Jul 2000
    Location
    Treasure Coast/Florida
    Posts
    9,754
    Copeland's Application Enginnering Bulletin AE-1287 tells you all about Demand Cooling. Pay particular attention to Fig.2 which gives you a rough idea of where it's needed with respect to your evaporating temp, condensing temp and return gas temp.
    Attached Images Attached Images

  9. #9
    Join Date
    Dec 2004
    Posts
    484
    Quote Originally Posted by markettech View Post
    Wise words - Not much more to add here.

    As painful as this is to me to admitt I also agree with dirtyboys post
    mark the date and time because we dont agree often
    except about the importance of regularly scheduled safety meetings

  10. #10
    Join Date
    Dec 2004
    Location
    Sunny So Cal!
    Posts
    649
    You need to check your discharge temperatures of your compressors- this is what your Demand Cooling module is attempting to correct. If you are running a high compressor suction temperature "superheat" your discharge temp will also tend to be higher. I have also seen poor oil viscosity influence this although I think the thin oil is more a product of the extreme conditions rather than the cause. You may need to open some TX valves to get a cooler temp to your comps- check the superheat! 20*f is noted as flooding, and 65*f is pushing too high ( as measured on comp. suction line- 6 " from comp)-
    the more saturated your return gas is the more efficient your comp will run - generally speaking.
    Run a bench test on them per Copeland but if they are all feeding sounds like a system issue to me.
    Look, just do your job, stay outta my way and we'll get along fine.

    Teach your kids to respect themselves and others with your actions- these little baboons will imitate you like it or not.