    404a Pressures

    The tag on my ice maker says high side pressure 500 and low-side pressure 250 is this correct ona commercial ice machine. Not familiar with 404A but that sounds high to me.

  2. #2
    Join Date
    Mar 2006
    Posts
    28
    Post Likes
    That has to be MAX pressures before something bursts.

    500 PSIG on 404A = over 150F

    250 PSIG on 404A = 110 F

  3. #3
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    14,771
    Post Likes
    Those are test pressures, all that means is that the circuits are rated to handle that much pressure. Normal operating pressure of 404 is nowhere close to that.

  4. #4
    Join Date
    Jun 2007
    Posts
    820
    Post Likes
    those are the max pressures rated for the evaporator and condensing coil, I pay attention to those when im using nitrogen for leak checks after i have installed a compressor or other.

  5. #5
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Post Likes
    Quote Originally Posted by couplux View Post
    The tag on my ice maker says high side pressure 500 and low-side pressure 250 is this correct ona commercial ice machine. Not familiar with 404A but that sounds high to me.
    Yup - a little high indeed. Water doesn't freeze well at +104F.

    Means you most likely will have a hand grenade sitting on top of a bin if the system pressures should ever go beyond those limits.