    If you have a 13 seer, 3 1/2 ton Carrier Puron system. Has a factory installed TXV installed on the evaporator. System pressure run 125 low side and 365 on the high side. Liquid line temperature reads 99 degrees which corresponds to the 11 degree subcooling required. After system pressures equalize and system is restarted the low side pressure will slower decrease, within 15 to 20 minutes the pressure will be down to 80 or 90 and will start frosting up all the way to the condenser. Head pressure stays the same and after 15 minutes the liquid line temperature starts dropping. TXV bulb is mounted correctly, there is adequate airflow across the coil. When the bulb is disconnected from the suction line the the same result. Just wondering what anyones answer to this problem would be.
    Jun 2001
    Louisville, KY
    Once you get into the frosty state, what are your superheat and subcooling readings? What is the return air wet bulb and dry bulb?
    Lower subcooling. Higher superheat. 80 degree dry bulb and 68 degree wet bulb.
    l
    Jun 2001
    Louisville, KY
    Is this an N coil? How long has it been installed?
    omaha
    Smile
    replace txv and try again
    It is an N coil. Has been installed 2 weeks. Homeowner says it ran too much and would never pull the temperature in the house below 80 degrees. Best temperature drop I got was 12 degrees.
    Replacing the TXV was what I was going to do, have one on order. For some reason there was not one on stock.
    Didn't know if there was something I was missing.
    Jun 2001
    Louisville, KY
    Does the coil fit the furnace or overhang? If it overhangs, which direction?
    I've seen N coils installed incorrectly (http://www.docs.hvacpartners.com/idc...m-cnpvp-01.pdf) as shown on page 4 in Alternative A and D. D is the worst. Most guys won't make a transition. So, C is the answer.
    I'm not saying the TEV isn't bad, but I'd look darn close at that coil first because it operates okay for a bit. Usually a bad TEV will pump down immediately. Your system is taking some time like some airflow is missing across part of the coil (Alternative D causes this).
    Jun 2001
    Louisville, KY
    Alternative D is the one with the WRONG label.
    The installer put the coil in the existing plenum since it was easier and the furnace was not replaced. Coil sits in the center of the furnace. When I saw the evaporator half covered in ice the first fix was fill in the 3 in gaps on each side of the coil, since air will take the easiest route around the coil. Its a 16" wide coil sitting in a 20" or bigger plenum.
    Jun 2001
    Louisville, KY
    Good chance the existing coil supports are covering the right side of the N. I have pics somewhere showing just that.
    There are a couple of places at the top of the N to shoot screws from the side instead of using support rails on that side.
    Good luck. Let us know what you find.