M# VVX
Comp 1 when loaded shuts off on hp.
60 suction 290 head
25 sh. 35 sc
Td 6f
H20 loop 4f
43 amps fla 47 amps

No signs of a restriction anywhere, I even replaced the power head and opened the txv.
When I shut off the hot gas bipass head pressure increases. Thought it was overcharged but there's no flood back.
Fock!

Thanks