Automated Logic BACview
I have a Automated Logic I/O 8168-R
that goes to a master then a BACview module.
It controls a chiller. Problem is it keeps tripping
on compressor fault. But upon resetting it,
everything seems fine for awile then it does it again.
Does anyone know what in the controller will cause
this fault?
-
07-10-2007, 09:33 AM #2
Regular Guest
- Join Date
- Jun 2007
- Posts
- 5
I/o 8168
This controller is made by OEM Control, a subsidiary of Automated Logic, for the chiller equipment manufacturer. Support and information should be available from the chiller manufacturer, as the controller was supplied by them.
Hope this helps.
-
07-15-2007, 05:25 PM #3
I'm thinking that you're headed in the wrong direction, the BacView is a tool to view the status and parameters on that module without having, or having to go to, the front end. Based on your description I think that you have a chiller problem, not a BacView problem.
HotRod
Controls..some days your a hero, some days your a zero. Direct acting since 1992.
-
07-16-2007, 08:20 PM #4
Waiting Email Confirmation
- Join Date
- Dec 2006
- Posts
- 183
Yes,
I know it is a mechanical problem but if
I knew what the fault was then it would point
the mechanic in the right direction.
Anyways, he came out and everything seemed
fine but we did sped up the tower fan because
it could be hi head pressure problem at times.
-
10-11-2007, 06:21 AM #5
Regular Guest
- Join Date
- Aug 2007
- Posts
- 11
or condenser water temp! check ur chiller operation
-
01-04-2010, 10:17 PM #6
New Guest
- Join Date
- Mar 2008
- Location
- delaware county pa
- Posts
- 3
Automated Logic BACview
check the electrolytic capacitors top middle of board there is three of them. One of them might be bad. I take care of a bunch of units which has these controllers and is a common issue. alarm says general fault comp# some timesbefore it even comes on. The way they wired these petra units was that a hi discharge pressre switch would cause that to. if one of those cap's happens to be bad it;s a easy cheap fix rather than buying a new board