    Soft Start or VFD for Trane RT

    Hello,

    I have a problem with a Trane YSC120A4RMA39D00000000000 D. The problem with it is when the blower kicks on it sounds like a ton of bricks is dropped on the roof. I've observed the operation for about a year and the belt and pulleys have to replaced every 6 months. The cycle times aren't short. It runs pretty good in that sense. I'm wondering if I can install a soft start relay or even a small Hitachi VFD would be an option to ease the starting to prolong belt and pulley life. What do you think?

    I was trying to do some research on the matter and was hoping Trane had something but, it seems they don't. I saw something online about "Soft Start Capacitor" but, googling that only yields soft start relays. Could I get some info on this item? Would that be the best seeing as a VFD inside a RT unit probably won't last in summer and winter temps.

  2. #2
    Join Date
    Apr 2012
    Posts
    94
    Post Likes
    If your changing your sheaves every 6 months, Then you have a serious misalignment going on. Sheaves aligned correctly should easily last 3-4 years.

  3. #3
    Join Date
    Jan 2007
    Location
    Stongsville Oh
    Posts
    1,410
    Post Likes
    Quote Originally Posted by 1SikLBZ View Post
    If your changing your sheaves every 6 months, Then you have a serious misalignment going on. Sheaves aligned correctly should easily last 3-4 years.
    I would first check into what has been stated. I also wonder about the cycle time that you referred to. I would think the supply fan would run continuous during occupied mode and then fan starts during unoccupied to maintain lo or high night setpoints. I think VFDs are a great upgrade for many applications. Noise at start would be eliminated wear reduced and starting amps greatly reduced. I would consider VFDs. Speeds can be adjusted for filter loading.
    ckartson
    I didn't write the book I just read it!

  4. #4
    Join Date
    Aug 2010
    Posts
    4,338
    Post Likes
    If its not cycling much but parts are getting chewed, its misaligned like ckartson said or the tension isn't right and its slipping.

  5. #5
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    if it is one of many up there might be counter rotating in the off mode from the building pressure rising up thru it
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  6. #6
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    Is this unit using an "a" or "b" belt?

  7. #7
    Join Date
    Apr 2012
    Location
    Texas
    Posts
    225
    Post Likes
    Verify alignment, Check for counter rotation, Quote a soft start and a VFD drive. Had a cooling tower once that liked to throw the drive shaft and people in the parking structure crapped their pants if they were near it. Soft start made repairs go away.
    Economy - Quality - Speed <---- pick two

  8. #8
    Join Date
    Mar 2010
    Location
    Kent, WA.
    Posts
    218
    Post Likes
    if you go with a drive you can mount it in the blower compartment and add a remote panel for the lcd in the electrical cabinet. the factory mounts them in this manner and I have done a few retrofits this way. the blower compartment will have better temps for the drive than mounting it outside in a electrical cabinet.
    forgot to mention, drives produce 3phase outputs. if you have a single phase unit you will need to change the blower motor and get the appropriate drive to run it on single phase.

  9. #9
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,380
    Post Likes
    Have you removed the rear panel and checked the rear bearing? That panel is a SOB to take off, so no one ever checks it.

  10. #10
    Join Date
    Nov 2013
    Posts
    14
    Post Likes
    Trane puts VFDs on most newer larger RTUs. You can pick up a TR200 from your local Trane parts center, and as someone posted earlier you mount it in the supply cabinet and run the display to the control cabinet. But in all honesty its sounds more likely that you have an alignment issue.

  11. #11
    Join Date
    Jan 2013
    Location
    Pacific NW,WA
    Posts
    11
    Post Likes
    Did we come to a conclusion on this issue? From reading posts I would be checking mechanical first? Good luck!

  12. #12
    Join Date
    May 2013
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by TEAMTRANE View Post
    Trane puts VFDs on most newer larger RTUs. You can pick up a TR200 from your local Trane parts center, and as someone posted earlier you mount it in the supply cabinet and run the display to the control cabinet. But in all honesty its sounds more likely that you have an alignment issue.
    Looking at the control display for that Trane VFD, that looks exactly like a Danfoss FC300 series display or LCP as Danfoss calls them. Since Danfoss is about an hour away, I'd like to see what they offer.




    Quote Originally Posted by MicronTech View Post
    Did we come to a conclusion on this issue? From reading posts I would be checking mechanical first? Good luck!
    No solution even 2 years later. It's not a high priority for anyone since the unit is only used for cooling since there's a condensing boiler and radiators for heating. We just figured out a different issue with the roof top unit. Everytime it would rain or outside had high humidity, indoors was swampy south Florida like. Turns out the OAD system i guess was set up for place like Arizona so, we would always be pulling outside air in regardless of outside humidity. I didn't personally change the setting but I guess there are different environment settings on the controller that were not set up correctly in the first place.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •