    I have a Carrier 48AKD060 and u cannot get the econ working. I have verified my parameters with tech support. The main base board was replaced due to the eeprom failing. The run status shows the "Supply Fan Not On 30s-yes" and this is locking out the econ. Now tech support is telling me this is a fixed algorithm (essentially a programmed time clock) and cannot be bypassed, change, etc. Here's the kicker, my supply fan has been running for 6 hours. Anyone know if that is true. I can't belive fan proving isn't done by a DP, or current sensor.
    Jun 2009
    StL, MO
    48AK should be a VAV unit - is this correct?
    What are your SFS.M and SFS.S settings?
    UA LU 562
    Apr 2011
    Chicagoland Area
    Yes, you are correct, it is a VAV.
    My SFS.S is set at NO
    My SFS.M is set at 0
    SE Pennsylvania
    Have you tried to SFS.M to 2 and allow the unit to use the duct DP transducer DP as fan proof. When set to 2 the duct DP must be greater than .20 with a 3 minute delay to prove the fan.
    Dallas ,Texas
    I think hvac69 may have fixed it for you Joe did tech although it sounds like you may have 3rd party controls on your unit. Your unit does have a DP switch which does have the ability to monitor fan status which may be disabling your economiser.
    I always liked to hardwired in a fan status using the VFD relay outputs.
    Quote Originally Posted by hvac69 View Post
    UA 100
    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.