    They write 50AMP max on the A/C lable for a reason

    This should do it.




    My Brother is digging into this after a property inspector found the burned up or corroded wiring, he didn't catch the 100AMP C/B, my Brother noticed that as he turned off the power to work on it.

  2. #2
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    On a side note they did use a HACR type breaker.

  3. #3
    Join Date
    Mar 2011
    Location
    Nw.Connecticut
    Posts
    307
    Post Likes
    Seems like it burned to the Ground wire , is that correct? Found RTU in the same fashion , 50apm max ,150 amp 3ph. 208 vac. breaker. Melted exploded contactor and wires...fed with #6 wire . What the hell Bobby?!

  4. #4
    Join Date
    Jun 2006
    Location
    SW MO.
    Posts
    5,610
    Post Likes
    I see 3 green wires.

  5. #5
    Join Date
    Apr 2010
    Location
    Red Deer, Alberta
    Posts
    661
    Post Likes
    Also looks like a bit of corrosion due to some high humidity or perhaps liquid contact? Water and electricity don't mix well...

  6. #6
    Join Date
    Jan 2005
    Location
    Jenison Mi
    Posts
    175
    Post Likes
    There, trip now you son of a.....

  7. #7
    Join Date
    Nov 2012
    Location
    Charlotte, Michigan 48813
    Posts
    145
    Post Likes
    Quote Originally Posted by VTP99 View Post
    On a side note they did use a HACR type breaker.
    Does Cutler Hammer / Eaton still make BR style HACR breakers?

  8. #8
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    Quote Originally Posted by taxman View Post
    Does Cutler Hammer / Eaton still make BR style HACR breakers?
    Yep

  9. #9
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,309
    Post Likes
    2 pole, 50 amp max

    2 x 50= 100.

    100 amp breaker it is!
    Every customer you take for granted today will be someone else's tomorrow.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •