Originally Posted by
mk#1in03
We have been having a problem with some baldor motors breaking there welded brackets and thus sending the fan blade through the condenser. I believe is has happened four times in the past year all on different condensers at different locations and all resulting in about a 1000lb recharge, last one was 1600#. Almost seems like the rivets are going bad on the blades throwing off the balance but when we check the other motors the blades seem fine. Has anyone seen similar issues or has anyone ever mounted a bracket underneath to try and stop the blade before it hits the coil?
have seen exactly what you had[probably 15 or 20], its allways a good idea to inspect the fan blades on the keeprite condensers, look for hairline cracks in the aluminum by the rivets. should be done regularly. its also a good idea to replace the blade with a motor change as if any slight bend in the aluminum blade may come to haunt you, they are not that bad in cost.
i dont think they are using the Baldor motors now but have moved to Marathon, not for the above reason but for many electrical winding failures in the baldors.
I have seen flat steel drilled out aqnd bent to mount with motor tab mounts and form a basket under the motor, think it was a custom job, looks like it wouldhelp
Mike