    goodman ckl-18-1

    2 units side by side one a goodman ckl-18-1. The other goodman ckl-18-1-b . The 18-1 nameplate states charge to 53 oz. R22. The 18-1 b nameplate states to charge to 72 oz R22. Units look identical. Both units cooling exact square footage. Same size air handler. Whats the difference between the two
    Quick reply to this message Reply  

  2. #2
    Join Date
    Dec 2003
    Posts
    2,851
    Post Likes
    The b needs 19 oz more refrigerent.
    Quick reply to this message Reply  

  3. #3
    Join Date
    Jul 2009
    Location
    kansas city, missouri
    Posts
    3
    Post Likes
    Thread Starter
    Thanks bigtime. I counted that up and still had one toe left. But I am wondering why
    Quick reply to this message Reply  

  4. #4
    Join Date
    Oct 2004
    Location
    Yakima, WA
    Posts
    1,847
    Post Likes
    Probably a new revision. Check the dates on the serial numbers - 10 seer vs 13 maybe? Is there another row of coils on the 'b' unit?

    19, huh? Fortunately men can count to 21. That's why we're better at blackjack than women.
    Quick reply to this message Reply  

  5. #5
    Join Date
    Jul 2009
    Location
    kansas city, missouri
    Posts
    3
    Post Likes
    Thread Starter
    Thank you CJP. My apologies for posting on the welcome thread. Good day everyone
    Quick reply to this message Reply  

  6. #6
    Join Date
    Oct 2013
    Location
    Sacramento
    Posts
    9
    Post Likes
    A new split system's condensing unit has enough refrigerant to accommodate up to a 30 ft line set typically, only after this point is it required to add additional amounts per additional line set and size etc. Some units have more coil surface area and will have a condensing temperature closer to ambient than a same BTU condensing unit with a smaller coil surface area, hence efficiency rating.
    A fixed metering device is a more critically charged unit as opposed to a modulating one such as a TXV valve that will have a receiver and can handle
    being overcharged a bit better than the fixed type that are dependent on the ambient temperature/pressure relationship of the unit and it's refrigerant used, For example:
    Under design conditions of 95F outdoors and 80F indoors and 50% humidity,..

    A normal efficiency R22 condensing unit will condense around ambient plus 30F , So 95F ambient plus 30F = 125F
    convert that 125F to pressure for R22 and you have 279#.

    A more efficient condensing unit with a large coil surface area might hold 8 lbs or R 22 and condense at ambient plus 25F !!

    Now for the indoors the TXV type will sense the suction lines temperature trying to maintain a 10F superheat about 1 foot after the evap coil, but no more than about 20F or so to the compressor if possible, as this is what cols the compressor besides the oil.
    A 80 F room will require a 40F evap coil to provide a Delta T (temp differential) of 20F for a 60F supply grille air temp.
    This is all design conditions and is ball park for the tecnicians with partially charged units
    Quick reply to this message Reply  

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •