    heat pump startup gone wrong

    First off, hi all. I got a 3ton h/p, change out with air handler and new lineset. I weighed the charge in according to nameplate and added extra for lineset, 11.85 lbs. On starting up the head was 145# and suct was 35#. 75 outdoor temp and 72 inside. Problem is when I checked sh it was high, around 30-35. So I started to add freon to lower it. Suction pressure started rising but instead of the suct temp dropping like it should to bring sh down the temp started rising! Any ideas would be great.

  2. #2
    Join Date
    Aug 2013
    Posts
    55
    If this 410a and a txv you need to wait at least 45 minutes of run time before adjusting the charge

  3. #3
    Its R22 with a piston. I did verify the correct piston size.

  4. #4
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    1,746
    What is your SC, delta T, WB, CFM? What is the calculated SH needed?

  5. #5
    Join Date
    Aug 2013
    Location
    Visalia California 93291
    Posts
    293
    Verify air flow before doing any refrigerant side testing what is your static and cfm

  6. #6
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    2,747
    why would anybody install a new 22 system

    see if your heat strips are on while cooling

  7. #7
    Join Date
    Sep 2013
    Posts
    18
    Make sure the piston is not in backwards.and check airflow , static pressure, cfm

  8. #8
    Join Date
    Jun 2001
    Location
    Moore, Oklahoma, United States
    Posts
    3,948
    Quote Originally Posted by Snapperhead View Post
    why would anybody install a new 22 system

    see if your heat strips are on while cooling
    Exactly..

  9. #9
    Join Date
    Dec 2005
    Posts
    1,823
    Quote Originally Posted by Jason4823 View Post
    First off, hi all. I got a 3ton h/p, change out with air handler and new lineset. I weighed the charge in according to nameplate and added extra for lineset, 11.85 lbs. On starting up the head was 145# and suct was 35#. 75 outdoor temp and 72 inside. Problem is when I checked sh it was high, around 30-35. So I started to add freon to lower it. Suction pressure started rising but instead of the suct temp dropping like it should to bring sh down the temp started rising! Any ideas would be great.
    Call an HVAC company out to fix it for you. That's is my best advice.

  10. #10
    Join Date
    Jul 2012
    Location
    Cincinnati ohio
    Posts
    234
    Quote Originally Posted by Chris1570 View Post
    If this 410a and a txv you need to wait at least 45 minutes of run time before adjusting the charge
    45minutes?

  11. #11
    Join Date
    Aug 2012
    Posts
    2,326
    diyer
    Trying not to be a Hack.

  12. #12
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,512
    When you started adding the refrigerant it started picking up heat ,add some more gas
    We really need change now

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event