    Trane residental 4 ton unit fan motor hot

    Ac cut out after a while of running ,I notice the fan motor housing getting very hot and shut down ,change motor 208 1/3 hp 1075 rpm the same thing happen motor getting hot and shutting down the unit with the new motor.

  2. #2
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,176
    Post Likes
    Quote Originally Posted by billcoburn View Post
    change motor 208 1/3 hp 1075 rpm

    208volt for residential? 208 Volt is usually 3 ph. I would call a Pro before you end up spending
    more money on parts, so he can trouble shoot the complete system.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  3. #3
    Join Date
    May 2007
    Location
    NC
    Posts
    66
    Post Likes
    Quote Originally Posted by mrbillpro View Post
    208volt for residential? 208 Volt is usually 3 ph. I would call a Pro before you end up spending
    more money on parts, so he can trouble shoot the complete system.
    208 single phase on outdoor residential.

  4. #4
    Join Date
    Jun 2007
    Posts
    17
    Post Likes

    Trane fan motor runs hot

    Ac cut out after a while of running ,I notice the fan motor housing getting very hot and shut down ,change motor 208 -230volt ac 1 ph 1/3 hp 1075 rpm the same thing happen motor getting hot and shutting down the unit with the new motor. I was told by an tech the rpm should be 825 rpm instead of 1075 rpm thanks :confused

  5. #5
    Join Date
    Jun 2007
    Posts
    17
    Post Likes

    ac fan motor cuts out

    Quote Originally Posted by kedalion View Post
    208 single phase on outdoor residential.
    208-230 single phase 1/3 hp 1075 rpm I was told by an tech it should be 825 rpm?

  6. #6
    Join Date
    Jun 2007
    Posts
    17
    Post Likes

    ac cuts out fan motor

    208volt for residential? 208 Volt is usually 3 ph. I would call a Pro before you end up spending
    more money on parts, so he can trouble shoot the complete system
    .

    I was told by an pro tech the fan motor is the wrong rpm should be 825 instead of 1075 agree??

  7. #7
    Join Date
    May 2007
    Location
    NC
    Posts
    66
    Post Likes
    what is the model number of the unit and I will tell what should be on it.

  8. #8
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347
    Post Likes

    *

    if you put a 1075 motor on a 825 blade you will for sure overamp the motor!



    .

  9. #9
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,347
    Post Likes

    *

    Quote Originally Posted by Airmechanical View Post
    if you put a 1075 motor on a 825 blade you will for sure overamp the motor!



    .
    and it will shutdown after it gets hot, until it finally burns out the new motor, if left on that application!



    .
    Last edited by Airmechanical; 06-12-2007 at 12:37 PM. Reason: *

  10. #10
    Join Date
    Jun 2007
    Posts
    17
    Post Likes

    ac fans runs hot

    what is the model number of the unit and I will tell what should be on it.

    The unit # is BDW-748A100A0 trane the fan was change about 4 mos.ago by an tech.

  11. #11
    Join Date
    Jun 2007
    Posts
    17
    Post Likes

    Wink ac fan motors runs hot

    [QUOTE=billcoburn;1514593]what is the model number of the unit and I will tell what should be on it.

    The unit # is BDW-748A100A0 trane the fan was change about 4 mos.ago by an tech. this is Information on the new blade 608151101,x38010348020,T12e102238.50cw three different #`s

  12. #12
    Join Date
    Jun 2007
    Posts
    17
    Post Likes

    ac fan shut down

    and it will shutdown after it gets hot, until it finally burns out the new motor, if left on that application!

    thanks the trane unit BDW-748A100A0 call for an 1075rpm 1/3 horse I will find the right pitch blade I hope where will i start looking .bill

  13. #13
    Join Date
    May 2007
    Location
    NC
    Posts
    66
    Post Likes
    MOTOR; 1/3HP, 200/230/60/1, 825 RPM, 48 FRAME, PERMANENT SPLIT CAPACITOR, SLEEVE BEARING
    This is what should be on the unit. Call a service tech and have it done the RIGHT way. Don't be cheap.
    The fan blade that you have on there now is the original blade for an 825 motor.