    anyone care to share some words of wisdom for heat loading comm kitchens? I have a customer wanting me to do one but not sure I want to go there. thx in advance
    Apr 2002
    Look in the ASHRAE handbook of fundamentals, they will give heat gains you can expect from the appliances, when they are vented by a hood or not.
    Not a lot of gain from the appliances under the hood as it is getting exhausted, the make up air is a big load.
    I always have the NEC in my mind when looking at other appliances. The electrically powered ones can be derated to 65% of the name plate according to the NEC when there are 6 or more appliances, this is conservative. Items like the refrigertors, freezers, refrigerated work tops etc.
    There is an email in my profile, if you got some drawings etc, I am doing a couple kitchens right now, could take a look at what you have if you wanted.
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.
    http://www.ductstrap.com/
    email address air to spare?
    should be
    in my profile...thx for your help
    Oct 2007
    Btu Output Means Btu Input