    kitchen heat loads

    anyone care to share some words of wisdom for heat loading comm kitchens? I have a customer wanting me to do one but not sure I want to go there. thx in advance

  2. #2
    Join Date
    Apr 2002
    Posts
    11,808
    Post Likes
    Look in the ASHRAE handbook of fundamentals, they will give heat gains you can expect from the appliances, when they are vented by a hood or not.

    Not a lot of gain from the appliances under the hood as it is getting exhausted, the make up air is a big load.

    I always have the NEC in my mind when looking at other appliances. The electrically powered ones can be derated to 65% of the name plate according to the NEC when there are 6 or more appliances, this is conservative. Items like the refrigertors, freezers, refrigerated work tops etc.

    There is an email in my profile, if you got some drawings etc, I am doing a couple kitchens right now, could take a look at what you have if you wanted.
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.

    http://www.ductstrap.com/

  3. #3
    Join Date
    Apr 2007
    Posts
    6,286
    Post Likes
    email address air to spare?

  4. #4
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793
    Post Likes

    should be

    in my profile...thx for your help

  5. #5
    Join Date
    Oct 2007
    Posts
    5
    Post Likes
    Btu Output Means Btu Input

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine