    Jun 2007
    Smile Confirming Condenser/Coil Match
    I am about to pull the trigger on a new Condenser and Coil combo installation and wanted to confirm with this board that the following is a correctly matched system. I am comfortable with the contractor, just wanted to double check the model #'s. Furnace is still in good shape.
    In Houston, 1800 sqft home. Built in 1994.
    American Standard Allegiance 14 - 410A 3 1/2 ton
    4A7A4042B1000A
    American Standard Horizontal Coil 3 1/2 Ton (with TXV installed)
    4TXFH041AS3HHA
    Replacing due to bad leak in the current evaporator coil (Carrier builder install).
    Thanks for any input.
    Jun 2007
    I'm NOT a HVAC tech but tonnage seems high for SF. Was a heat calc done?
    ARI Ref #: 672834
    http://www.aridirectory.org/ari/
    AMERICAN STANDARD, INC. Allegiance
    144A7A4042B1
    4TXFH041AS3
    41,500: BTU/H
    10.80: EER
    13.00: SEER
    1RCU-A-C: ARI Type
    $274: Cooling Cost
    Jun 2007
    Well, how about that!
    Thanks for the info.
    Littleton MA
    Quote Originally Posted by vrocrider View Post
    Not too sound rude, but if you are not a tech or in the field you really shouldn't comment.Your question is right on about the calc, but how do you know what sounds too big?
    We only want to do it, if we can do it right.
    Jun 2007
    No offense taken.
    I live in Atlanta in 1700SF house with 3 ton unit and I'm battling an oversize issue. Just trying to help someone else living in similar size house in similar geography not make the same mistake i did; i.e take the word of contractor saying I need to upsize to 3 ton WITHOUT heat load calc.
    This board's help me in the few days I've viewed. Just trying to give back what little I can.
    See my thread on heat load calc.