Results 1 to 7 of 7
    Jun 2007
    New 10SEER condenser with existing 8SEER Coil?
    Any problem installing new 10SEER 5 ton condenser with existing 8SEER Evap coil? Thanks.
    Massachusetts
    10 SEER? From Where?
    I can't imagine anyone having a new 10-SEER unit still in inventory. What I can tell you is that if it's an AC only unit, it will work but the SEER rating actually achieved will probably somewhere in the 8.5 area. A new evap coil is highly recommended. However if the unit is a heat pump, I wouldn't do it without replacing the indoor coil. An R-22 heat pump with an undersized coil will blow the high side pressure up over 500 PSIG when you switch to heating and the internal pressure valve will open in the compressor. Simply put it probably won't work on a heat pump.
    Florida
    Add a txv. It should dehumidify well. Seer rating is tossed out the window, but if you're in an area with inexpensive electric and a cooler climate, why not use it. This isn't saying I don't prefer a new matched system.....
    Jun 2007
    Why add TXV? Thanks
    Florida
    Quote Originally Posted by vrocrider View Post
    Why add TXV? Thanks
    With a mis-matched system, this controls the system's superheat, and adjusts according to the load on the coil, running more effeciently while preventing floodback to your compressor(slugging).
    Jun 2007
    Thanks. This is installed at and outside the coil? Rough cost for part for 5T?
    Florida
    They can be installed inside the cabinet or outside the cabinet. Due to rules, can't help you with cost, your A/C man can tell you.