Thread: New ac system and humidty

  1. #1
    Join Date
    May 2007
    Location
    East coast
    Posts
    27
    Post Likes

    New ac system and humidty

    Just had a new American Standard ac system installed. It's a 3 ton 13 seer unit in a 1600 sq. ft. brick home built in 1960.
    The temperature can be set at 76 degrees - feels fine when the system is running, but shortly after the air feels somewhat humid.
    Is the system oversized? We haven't had weather above 90 degrees as yet.

  2. #2
    Join Date
    Jun 2007
    Location
    RI
    Posts
    121
    Post Likes

    who sized it?

    Who sized the unit? Are you going to add on to the house? It seems pretty big even for a poorly insulated home that size. That will keep the humidity high because the unit will drop the temp like a rock when it turns on then shut off fast.

  3. #3
    Join Date
    Sep 2006
    Posts
    1,255
    Post Likes
    Several things can be causing this. If you keep your fan in the ON position the moisture that is on the evaporator coil when the unit cylces off will be re-absorbed by the air passing over it. If the condensate pan isn't draining very quickly same thing. A lot of peole prefer the AUTO position during cooling periods.

    Secondly, how was the 3 ton size determined? If anything other than manual J, then it may not be right. Was there an A/C unit before this one? What size was it?

  4. #4
    Join Date
    May 2007
    Location
    East coast
    Posts
    27
    Post Likes
    Thread Starter

    new ac system and humidity

    There was a 3 ton unit prior to the new. I don't think a Manual J was done.

  5. #5
    Join Date
    Sep 2006
    Posts
    1,255
    Post Likes
    Did the old unit do better than the new one with de-humidification?

    Did you get a new air handler too or just a new coil over your furnace?

  6. #6
    Join Date
    May 2007
    Location
    East coast
    Posts
    27
    Post Likes
    Thread Starter
    Yes, I do belive the old did a better job with humidity. I did have a new air handler installed.

  7. #7
    Join Date
    Feb 2004
    Posts
    43
    Post Likes
    it could be the new higher seer rating, may not be removing the mositure that the old 10 seer did. you may need to lower the tstat a couple of degrees than you did before , and run the fan on a lower speed to do more laten cooling, lower the humidty.
    also look up seer rating on this site you might see whats really going on. hope this helps....

  8. #8
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    A-S units if on a matched A-S coil have a good latent capacity rating BUT new units do take longer to get to full moisture sucking rate. So you may have gotten by with a 3 ton for 1600 sq ft in the past but may not with today's units. Without doing a load, hard to say if that's oversized but sure sounds like it.

    And I sure agree with the advice to not run the blower constantly, put it in auto!

  9. #9
    Join Date
    Sep 2006
    Posts
    1,255
    Post Likes
    First thing I would do is confirm all the settings for the air handler. If it is a variable speed unit then it can be configured in different ways. Make sure that it is setup for 3 tons and for maximum humidity removal. Call your installing contractor back and tell him of your concerns and ask him to check everything out.

    Also, if you don’t already have one, have your contractor install a humidistat (either separately or a new t-stat that is also a humidistat) that will allow more control of your variable speed blower. With a humidistat, the fan speed will be slowed down further to help with moisture removal when the temps are not high enough to call for cooling. It will allow your a/c to act somewhat like a whole house de-humidifier.

  10. #10
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by mchild View Post
    . With a humidistat, the fan speed will be slowed down further to help with moisture removal when the temps are not high enough to call for cooling. It will allow your a/c to act somewhat like a whole house de-humidifier.
    Moisture on the cooling coil slowly re-evaporates back in the ducts and home. 13 seer coils hold 6-8 lbs. of moisture. Re-evaporate 3 lbs. of moisture raises humidity 10%RH.
    Forget the dehumidistat and slow the fan to max the moisture removal all the time. Getting the home dried down during high hours of a/c helps some for evenings and rainy days. Your home will still be too damp during a wet week. If your home gets too dry, let us know.
    Dehumidistats can lower fan speed or over-cool. They never "allow your a/c to act soomewhat like a whole house dehumidifier". With a whole house dehu, you get the %rh you set independent of the a/c operation or without any a/c over-cooling. I am tracking a 2,400 sqft home. Remove 3-4 gallons everyday to maintain 50%RH. No ac for weeks now in Midwest. Tring to do this with a/c would be impossible and very inefficient. Whole house dehu and 13 seer a/c cost about the same two speed a/c, but more eff. and comfortable. Dehu TB

  11. #11
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes

    Thumbs up Thanks to TB's posts...

    I added a 35-pint dehum in my 1600 SF walkout basement. Setpoint is 55&#37;. Cycles 50 to 60%. Upper level is staying <45%. Couldn't do that last fall without the dehum.
    Perhaps you should have read the instructions before calling.

  12. #12
    Join Date
    May 2007
    Location
    East coast
    Posts
    27
    Post Likes
    Thread Starter
    Is a variable speed air handler necessary for a humidistat?

  13. #13
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes
    Quote Originally Posted by RobertD View Post
    Is a variable speed air handler necessary for a humidistat?

    No, but it makes it easy to connect one.
    Quality and Value Service and Repair

  14. #14
    Join Date
    May 2007
    Location
    East coast
    Posts
    27
    Post Likes
    Thread Starter
    Thanks to all. This is a great site!

  15. #15
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by jrbenny View Post
    I added a 35-pint dehum in my 1600 SF walkout basement. Setpoint is 55%. Cycles 50 to 60%. Upper level is staying <45%. Couldn't do that last fall without the dehum.
    Thank you for your comment and welcome to first level of the "dehu club". A small inefficient dehu is a start and adequate for low humidity loads. You have unusually low outdoor points for the last 6 weeks. Higher humidity loads are on the way. http://www.weather.com/maps/maptype/...nts_large.html
    This site will give you an idea of the moisture loads headed your way. The next level is being able to maintain <50%RH throughout your home with a +70^F outdoor dew point and rain(low or no cooling load).

    Another level up-- Most homes like yours do not have adequate fresh infiltration during the summer when compared to winter stack effect. So consider adding 50-75 cfm of fresh air ventilation when occupied to purge indoor pollutants and renew oxygen. This is minimum fresh air according to ASHRAE. This bumps up the dehumidification load. On the wettest day with low/no cooling and +70^F outdoor dew points, you need to remove 60-80lbs. of water to maintain 50%RH. The highest level of the “dehu club” should include 5-6 lbs. of moisture per KW verses the 1-2 lbs./KW of your current dehu. Good start! Watch for the high outdoor dew points. They can get upto +89^F. Dehu TB

  16. #16
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Baby steps, TB. Baby steps.

    It may cost a bit more in the long run, but I want to step into the larger ones to actually measure true performance.

    Part of the comfort is the 2-stage cooling and Infinity control.

    Next step is definitely fresh air intake and a larger dehum.
    Perhaps you should have read the instructions before calling.

  17. #17
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes
    Quote Originally Posted by teddy bear View Post
    Moisture on the cooling coil slowly re-evaporates back in the ducts and home. 13 seer coils hold 6-8 lbs. of moisture. Re-evaporate 3 lbs. of moisture raises humidity 10%RH.
    Forget the dehumidistat and slow the fan to max the moisture removal all the time. Getting the home dried down during high hours of a/c helps some for evenings and rainy days. Your home will still be too damp during a wet week. If your home gets too dry, let us know.
    Dehumidistats can lower fan speed or over-cool. They never "allow your a/c to act soomewhat like a whole house dehumidifier". With a whole house dehu, you get the %rh you set independent of the a/c operation or without any a/c over-cooling. I am tracking a 2,400 sqft home. Remove 3-4 gallons everyday to maintain 50%RH. No ac for weeks now in Midwest. Tring to do this with a/c would be impossible and very inefficient. Whole house dehu and 13 seer a/c cost about the same two speed a/c, but more eff. and comfortable. Dehu TB


    I could not disagree more with this statment.
    Quality and Value Service and Repair

  18. #18
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Quote Originally Posted by Freezeking2000 View Post
    I could not disagree more with this statment.
    Why? Just curious.
    Perhaps you should have read the instructions before calling.

  19. #19
    Join Date
    Jul 2001
    Location
    Fairfield and NewHaven Counties in Commecticut
    Posts
    4,982
    Post Likes
    Quote Originally Posted by Freezeking2000 View Post
    I could not disagree more with this statment.
    I changed my air handler and had to set the blower as low as it dould go to remove as much humidity as my old 2 ton airpro with a 1/6 HP blower motor.

    I am telling you to have the installers check your unit.
    Quality and Value Service and Repair

  20. #20
    Join Date
    Jun 2007
    Location
    south carolina
    Posts
    176
    Post Likes
    13 seer have more fins per square inch then ten seer ten seer was an outstanding dehuimidifier dont use small room dehu's they dry a small area and moisture always moves to dry air but it dosent turn corners just goes right through your walls possibly causing mold in the walls. The manual j has to be done before anything and then use either whole home dehu or two stage compressor with variable speed a/h

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •