    I have a Varitrac CCPII that the company inherited along with some timers to shut it down on the weekends. my question is what is the voltage that should be going into the unoccupy terminals.

    Thanks

  2. #2
    Join Date
    Feb 2006
    Location
    Atlanta,GA.
    Posts
    959
    Post Likes
    no voltage, just NO contacts, voltage is from ccp