    New air handler install; compressor stops running

    I had a new Trane air handler installed last week and the unit has been working very well. But, for some reason the compressor in my heat pump stops running for a certain time period multiple times a day. When the compressor stops, I notice:
    1. Thermostat is set and active in "cool" mode
    2. Air handler fan speed is high
    3. Warm air coming out of vents
    4. Condenser(?) fan is still running in heat pump


    Is this normal? The heat pump I have is 2.5 tons.

    Thanks in advance for any help.

    Mike

  2. #2
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    What's the model number of the heat pump? How old is it?

    I suspect a recip compressor and no hard start kit added. Just an internet guess.
    Perhaps you should have read the instructions before calling.

  3. #3
    Join Date
    May 2007
    Posts
    20
    Post Likes
    Thread Starter
    Heat pump brand is a Unitary Product Group (york?), model BRHS0301BD. Heat pump is ~ 5 years old and is a 10 seer according to the book.

    Why would I need a hard start kit? I never had a problem before the new air handler was installed.

  4. #4
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Yep. Recip compressor. The Trane air handler has a non-bleed thermal expansion valve. Compressor isn't starting every time due to non-equalized pressures.

    Contractor needs to add a hard start kit.
    Perhaps you should have read the instructions before calling.

  5. #5
    Join Date
    Dec 2006
    Location
    Middle Tennessee
    Posts
    11,346
    Post Likes

    *

    Quote Originally Posted by mike2007 View Post
    Why would I need a hard start kit? I never had a problem before the new air handler was installed.


    EXACTLY!

    ya probably have a txv on the new a/h

    whats the model # on the new a/h



    .

  6. #6
    Join Date
    May 2007
    Posts
    20
    Post Likes
    Thread Starter
    Model of the air handler is 2TEE3F31A1000AA. Not sure what a thermal expansion valve is, but appreciate the insight. I'll see what the contractor says.

    The previous air handler was a comfortmaker (~ 23 years old). How is the new setup different where I need a hard start kit? I have a curious mind, so if you wouldn't mind explaining I'd appreciate it!

    Thanks.
    Last edited by mike2007; 05-30-2007 at 04:16 PM.

  7. #7
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,976
    Post Likes
    Is the outdoor unit going off for about 10 minutes each time? If so, the outdoor unit may be going into defrost. Defrost timers normally start defrost every 30, 60, or 90 minutes. Sounds like a shorted defrost thermostat.

    Note also your outdoor unit should match the indoor unit & visa versa. You should change the outdoor unit to match the new indoor unit for best results.
    Remember, Air Conditioning begins with AIR.

  8. #8
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Your old air handler had a piston for metering refrigerant. Pressures could rapidly equalize on shutdown. The new air handler has a hard shut off TEV. Pressures take a very long time to equalize.

    Good discussion on why you need a hard start kit:

    http://hvac-talk.com/vbb/showthread.php?p=1459833
    Perhaps you should have read the instructions before calling.

  9. #9
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Quote Originally Posted by Kevin O'Neill View Post
    Is the outdoor unit going off for about 10 minutes each time? If so, the outdoor unit may be going into defrost. Defrost timers normally start defrost every 30, 60, or 90 minutes. Sounds like a shorted defrost thermostat.

    Note also your outdoor unit should match the indoor unit & visa versa. You should change the outdoor unit to match the new indoor unit for best results.
    I thought about that, but he stated the ODF is running.
    Perhaps you should have read the instructions before calling.

  10. #10
    Join Date
    May 2007
    Posts
    20
    Post Likes
    Thread Starter
    Quote Originally Posted by Kevin O'Neill View Post
    Is the outdoor unit going off for about 10 minutes each time? If so, the outdoor unit may be going into defrost. Defrost timers normally start defrost every 30, 60, or 90 minutes. Sounds like a shorted defrost thermostat.

    Note also your outdoor unit should match the indoor unit & visa versa. You should change the outdoor unit to match the new indoor unit for best results.
    I didn't actually time it, but after a little while the compressor does go back on. I immediately thought to myself "why is this in defrost mode?" when I first noticed because it's doing exactly what it would do in the winter. Also, I noticed the liquid line (smaller) was colder than the vapor (larger) line, if that means anything...

    The indoor unit is a 13 seer while the outside is a 10 seer. I know this isn't the most efficient, but this also probably means the outside unit will cycle more?

  11. #11
    Join Date
    Mar 2007
    Location
    Myrtle Beach, SC
    Posts
    2,976
    Post Likes
    Sounds like a bad defrost thermostat.

    Why did you change the unit?
    Remember, Air Conditioning begins with AIR.

  12. #12
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Does the outdoor fan continue to run during this evolution as you stated in the original post? If so, it's not a defrost issue.
    Perhaps you should have read the instructions before calling.

  13. #13
    Join Date
    May 2007
    Posts
    20
    Post Likes
    Thread Starter
    Sounds like a bad defrost thermostat.

    Why did you change the unit?
    Could the contractor have shorted the thermostat? He did change wiring outside also.

    The old unit was replaced because it would constantly get "stuck on" and the indoor coils would ice up and the heat pump would run continuously. Also, the fan stopped starting on it's own (motor was shot) and before we bought the house the coils were packed with dirt. Cleaned them out several times, but the air flow just wasn't good like it is now.

  14. #14
    Join Date
    May 2007
    Posts
    20
    Post Likes
    Thread Starter
    Quote Originally Posted by jrbenny View Post
    Does the outdoor fan continue to run during this evolution as you stated in the original post? If so, it's not a defrost issue.
    Yes, outdoor fan continues to run. At the same time, the air handler fan is running.

    I did read the post that explains txv's and a poster was talking about "time-off delays". The air handler that was installed is variable speed and there's mention in the book for a "cooling off delay" where the compressor would shut-off and the fan would continue running, but does that only apply to the inside fan?

  15. #15
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,855
    Post Likes
    Yes, indoor fan only.

    Call your contractor. Regardless of our guesses, you have system issues.
    Perhaps you should have read the instructions before calling.

  16. #16
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    Quote Originally Posted by jrbenny View Post
    Yep. Recip compressor. The Trane air handler has a non-bleed thermal expansion valve. Compressor isn't starting every time due to non-equalized pressures.

    Contractor needs to add a hard start kit.
    \



    agree 100%....

    call contractor back before compressor is damaged.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •