Can this unit be repaired? Pics inside...
HERE is my 1993 3-ton Trane XE1200 heat pump.
The compressor hasn't been working so I had a technician out for a diagnosis. THIS is what he discovered when he took the access panel off. HERE is a closer look.
So I'm missing 11 lbs of R22 and it's not cooling too well right now.
Questions:
- Is the break in that tubing repairable...or does the entire assembly need to be replaced?
- Since this unit has no low-pressure cut-off switch, what did the compressor do when all the R22 leaked out? Did it keep running until it self-destructed?
- Is it likely that the compressor has suffered serious damage?
I hate to say it...but I'm the typical homeowner... If I can have this unit repaired and limp it through this season with a reasonable (better than 50%) chance of success, I'll try it. But if you guys tell me to stick a fork in it, I will.
Thanks for any advice.
-
05-24-2007, 06:36 PM #2
Repairing the stub is easy.
Chances of the system being reliable afterwards slim.
Depending how long it was like that, the compressor could die the day after they got it running.
Pull the fork out, you'll see it done.
-
05-24-2007, 06:37 PM #3
Regular Guest
- Join Date
- Apr 2005
- Location
- Tampa, Florida
- Posts
- 1,631
Um...shut that unit off immediately and get a service tech out there!!! The compressor might have been damaged from running without refer in there, but it's difficult to say. Only a service tech on-site can make the judgement call. If the compressor's functional, that unit can easily be repaired. The break is in the copper and not the aluminum, so you should be in good shape. Again, much depends on the state of the compressor. Depends how long the refrigerant line has been broken, how much moisture has got in there and how long the compressor tried to run. When it comes time to replace it (which may be soon), pony up the extra money for a unit with a low pressure switch. My AC condensing unit got absolutely nailed by Hurricane Charley, moved about 6", ripped through the hurricane straps, and ended up jamming one of the screws from the hurricane straps into the condenser coil. A low-pressure cut-out switch prevented any major damage. The coil was replaced and the system's been running fine since then...with different hurricane straps.
-
05-24-2007, 06:51 PM #4
the repair is easy but how many are going to be needed
once the tubing starts to leaks others soon follow
personal experience. The repair is temp at best till a new unit can be installed or coil replaced
-
05-24-2007, 06:59 PM #5
Regular Guest
- Join Date
- May 2007
- Posts
- 71
I've received conflicting opinions up to this point from different contractors. Some have said it's toast. Others have said it may be OK. Can a technician do some preliminary tests to assess the condition of the compressor...or are they going to have to toss 11 lbs of refrigerant in it and just try to fire it up?
The estimate to repair this unit is less than the new air cleaner I'm being quoted in my replacement system...that's why I'm torn about taking a gamble on just fixing it.
On a side note... I'm familiar with automotive AC systems and was blown away to learn that most home systems apparently don't have a low pressure switch to protect the compressor???
-
05-24-2007, 07:01 PM #6
2 months ago I found a unit that had done the exact same thing.
If it broke in the heating mode and ran that way for a while, the system will have sucked in a lot of air and moisture.
On the one I found, I cut the vapor line open and found that "green slime" had formed in the system, so we had to replace the whole system, including the refrigerant lines. There is no cleaning up the green slime.
If more government is the answer, then it's a really stupid question.
-
05-24-2007, 07:06 PM #7
Add the cost of repairing it, to the cost of replacing it.
Do you really want to gamble that much money.
-
05-24-2007, 07:09 PM #8
Regular Guest
- Join Date
- May 2007
- Posts
- 71
-
05-24-2007, 07:09 PM #9
Yes it can easily be repaired. Green slime is possible, It depends on how long it ran while empty. If you were home when it failed and shut it off right away, you have a good chance. It also depends on local humidity levels. More moisture sucked in = more problems. It looks to me like it broke from vibration. The braze joint did not fail, the pipe broke.
Remember, Air Conditioning begins with AIR.
-
05-24-2007, 07:18 PM #10
That is an easy repair, but since it broke in the heating mode, it will have pulled in a lot of air, and associated moisture.
Before repairing something like that, I always cut the refrigerant lines open between the wall and the unit, and cut a couple of tubes open inside the unit to inspect the inside of the lines.
Any green at all on the walls of any tubing or in the refrigerant oil, and the entire outdoor unit, refrigerant lines, and indoor coil are scrap, none of it can be saved.
If it had broken in the cooling mode, it wouldn't pull in any air because that part of the system would be on the high pressure side.If more government is the answer, then it's a really stupid question.
-
05-24-2007, 07:31 PM #11
Regular Guest
- Join Date
- May 2007
- Posts
- 71
Interesting. Nobody has mentioned this to me before.
Let me ask a related question...
If you guys were replacing this system, would you insist on replacing the lineset? I've had one Trane contractor say he would just flush the lines and install a filter. Is that legitimate in this case? My lineset isn't easily accessible...but it could be replaced with a little effort.
-
05-24-2007, 07:47 PM #12
If the system developed any "green slime", the lineset needs to be replaced. There is no flush that will remove it, and it will contaminate the new system.
If more government is the answer, then it's a really stupid question.
-
05-24-2007, 07:50 PM #13
We replace the line sets 98% of the time on our swap outs.
Your is one that we would flush as a last resort only.