    40 gallon gas with a vent motor FGR
    the thermocouple screws into a factory interrupt switch
    that connects to two limit switches on the top flue vent opening
    I have continuity through the wire and both limit swiches, but
    when i connect the limits back into the switch the pilot does not stay lit
    If I jump out the switch the PILOT will stay on
    Can it be a weak thermocouple that does not
    generate enough current to travel through the limits?
    The pressure swich is working and it energizes the vent motor when
    the burner lights
    PDX
    Check the voltage of the Thermocouple. If it is out of the acceptable range, its bad.
    Jul 2002
    NorthEast
    Should I check the Voltage at the terminals that are behind the
    control vave
    What is an acceptable milivolt reading for that valve