Thread: how often do professionals really do manual J tests?

  1. #1
    Join Date
    Jun 2006
    Posts
    40
    Post Likes

    how often do professionals really do manual J tests?

    I read all the time that your contractor should perform a heat/cooling load calc, and if not you should find someone else who will, but over the past few years I've had several contractors out for a couple of different projects (including installing central air for the first time), and NOONE is crunching those numbers. I even asked this last time and received the "I've done 800,000 of these.......". But when the units come in increments of 1/2 tones, what's the practicality of such a calculation anyway? Or is more than sizing the unit, like number of supplies/returns, where they are located, etc.?

    Thanks!

  2. #2
    Join Date
    Sep 2006
    Posts
    1,255
    Post Likes
    They like to do them about as much as my ten year old son likes to take a shower.

    But without one they are guessing. There are just too many factors that influence the answer. That is why most residential systems are over sized. They guess and go big so that they aren't as likely to get a call back. But it ends up costing you more for the equipment and more to operate. Plus, if you are in an area that has high humidity then it will likely leave you with a more humid house and you won't be comfortable. This is your first A/C (at least in this house) don't get it wrong after waiting this long.

    For $50 you can do your own. Go to the top of this web iste page and click on the HVAC-Calc link. It is money well spent.
    Last edited by mchild; 05-21-2007 at 06:14 PM. Reason: Started Thinking

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    A room by room manual J will tell you how many CFM each room needs.
    Manual D can then be done to tell what frition rate to use for sizing the duct work.

    When done right.
    Helps prevent those rroms that are too cold or hot.

  4. #4
    Join Date
    Jun 2004
    Location
    4H: Hot, Humid Houston H.O.
    Posts
    3,304
    Post Likes
    I agree, it's hard to find a pro who will do Manual J, at least that has been my experience for an existing house. I wanted to really find out whether I had the right size AC (not to mention we were seriously confused about what size was installed, due to illegible labels). There was one AC pro who sure seemed conscientious, and old-school hard duct metalworker kind of guy. Father and son in business together, the older guy took some room measurements and told me I needed 4 tons on one side of the house and 5 tons on the other. Naturally that required a complete redo of the duct work too.

    I don't doubt the sincerity of that guy but he was *so* far off on sizing. Where he prescribed 4 tons I had at the time 3.5, and have downsized to 3.0 with good results -- I really suspect 2.5 might be the closest fit. Where he prescribed 5 tons I now have 3.5 and I expect this summer may prove that is more than needed.

    My Hvac-Calc Manual J7 showed 5.0 tons approximately required, depending on what value I chose for infiltration. Since that is across two halves of the house, and the halves peak at different times, each half must be sized appropriately for its own peak demand. Manual J8 does a better job of estimating duct losses, than J7, so I found myself having to guess at that component of cooling load. The overall experience has taught me the shortcomings of an amateur like me trying to provide all the info for an important model -- but I suggest to anyone it is better than your other choices. The program is easy to work too, only took me a couple hours and most of that time was measuring walls and windows.

    One caveat about Hvac-Calc, it is no substitute for using Manual D for airflow. You will get only rough ballpark air flow numbers if you omit Manual D. I predict your typical pros will fall back on "I've done 800,000 of these" when you ask them about Manual D, deja vu all over again<g>. If you find a pro who actually will use Manual D, he's a keeper no matter what he charges!

    Hope this helps -- Pstu

  5. #5
    Join Date
    Jul 2002
    Location
    Zelienople, Pa
    Posts
    2,965
    Post Likes
    Quote Originally Posted by pstu View Post
    If you find a pro who actually will use Manual D, he's a keeper no matter what he charges!

    Hope this helps -- Pstu
    Wow, if 25% more of my leads would believe this, I would rule this town...

    I do a manual J & D on 90% of the homes I estimate.

    The other 10% are for landlords, Asians, or Middle Eastern folks and I'm not wasting my time...
    How tall are you Private???!!!!

  6. #6
    Join Date
    Jul 2005
    Posts
    717
    Post Likes
    Quote Originally Posted by Gunnery Sergeant Hartman View Post
    Wow, if 25% more of my leads would believe this, I would rule this town...

    I do a manual J & D on 90% of the homes I estimate.

    The other 10% are for landlords, Asians, or Middle Eastern folks and I'm not wasting my time...
    ************************************************** ********
    wow, Imo you are not only an hvac guy you are a racist.

  7. #7
    Join Date
    Mar 2004
    Location
    SE Michigan
    Posts
    24,816
    Post Likes
    Around here, you need one if your going to pull a permit. The inspector will ask you, how do you know thats the size of a furnace or a/c you need?...and you have to be able to show them.

  8. #8
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    we don't need them for permits............yet.

    we do need them for rebates, most of the equipment we sell is high efficiency so they all get load calcs done.

  9. #9
    Join Date
    Jun 2006
    Posts
    40
    Post Likes
    Thread Starter
    wow. interesting point. hadn't even thought about a permit. do i need one (or want one) for installing central air and/or new heating?

  10. #10
    Join Date
    Mar 2007
    Location
    Phoenix, AZ
    Posts
    574
    Post Likes
    Quote Originally Posted by deejoe View Post
    Quote Originally Posted by Gunnery Sergeant Hartman View Post
    I do a manual J & D on 90% of the homes I estimate.

    The other 10% are for landlords, Asians, or Middle Eastern folks and I'm not wasting my time...
    ************************************************** ********
    wow, Imo you are not only an hvac guy you are a racist.
    Same reaction I had...

  11. #11
    Join Date
    Jun 2004
    Location
    4H: Hot, Humid Houston H.O.
    Posts
    3,304
    Post Likes
    >>I do a manual J & D on 90&#37; of the homes I estimate.
    >>
    >>The other 10% are for landlords, Asians, or Middle Eastern folks and I'm not wasting my time...

    Maybe "stereotypist" would be a better word. This is not someone who goes out and lynches people, after all. Nor an Aryan supremist type, at least not evidenced so far. There are degrees of malice in ethnic stereotyping and I would not slam this man with the worst.

    But if you take out the convenient cliche then it's not so easy to stop thinking about something.

    ARP board, anyone?

    Best wishes -- Pstu

  12. #12
    Join Date
    Mar 2007
    Location
    Phoenix, AZ
    Posts
    574
    Post Likes
    Quote Originally Posted by pstu View Post
    This is not someone who goes out and lynches people, after all. Nor an Aryan supremist type, at least not evidenced so far.
    Agreed there are degrees. From genocide to tending to evaluate circumstances based on race.

    The use of stereotypes based on race as represented by the poster is a way to judge groups of people based on race in advance of dealing with any one individual from that group. In this case, it amounts to not doing business with certain specific racial/ethnic characteristics. Sorry - that's racism.

  13. #13
    Join Date
    Jun 2005
    Location
    The Gray Northwest
    Posts
    661
    Post Likes
    Quote Originally Posted by CottyGee View Post
    Agreed there are degrees. From genocide to tending to evaluate circumstances based on race.

    The use of stereotypes based on race as represented by the poster is a way to judge groups of people based on race in advance of dealing with any one individual from that group. In this case, it amounts to not doing business with certain specific racial/ethnic characteristics. Sorry - that's racism.
    Okay, simmer down. We all have our life expieriences and in this country, we are supposed to be able to talk about it freely.

  14. #14
    Join Date
    Mar 2007
    Location
    Phoenix, AZ
    Posts
    574
    Post Likes
    Quote Originally Posted by big johnson View Post
    Okay, simmer down. We all have our life expieriences and in this country, we are supposed to be able to talk about it freely.
    Exactly. And when someone posts a racist comment, I'm allowed to talk about it.

    By the way, I don't think I need to "simmer down". That presumes I'm about to blow a gasket. I'm not. I'm just spotlighting an issue - nothing more, nothing less.

  15. #15
    Join Date
    Jun 2005
    Location
    The Gray Northwest
    Posts
    661
    Post Likes
    Quote Originally Posted by CottyGee View Post
    Exactly. And when someone posts a racist comment, I'm allowed to talk about it.

    By the way, I don't think I need to "simmer down". That presumes I'm about to blow a gasket. I'm not. I'm just spotlighting an issue - nothing more, nothing less.
    What do ya say we stick with HVAC in our debates?
    Have a great day....

  16. #16
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Freedom of speech should be used with restraint.

  17. #17
    Join Date
    Jan 2006
    Posts
    49
    Post Likes
    Back to topic:

    I do load cals for all new work(required for permit). I do manual D because you have to know correct ductsize to install(this goes to my guys and some cities require for permit).

    Replacements(permit required but not cals): This is the hard part. Replacing old systems or just one unit with higher SEER units gets tricky. Refrigerant line sizes, duct work and electrical have to be looked at closely, a mistake here can cost me a bunch of bucks. Load cals and duct sizing are not a must but if there is a question I do one.

  18. #18
    Join Date
    Aug 2002
    Location
    Southern NJ
    Posts
    962
    Post Likes
    I do them alot just to make sure the existing system is the correct size. I also believe that air balancing is just as important to having the correct size unit. I've seen so many systems that were properly sized that ran like junk because the house wasn't balanced at all.

  19. #19
    Join Date
    Jan 2006
    Posts
    49
    Post Likes
    You have to balance system to see if if the air flow is up to manual D or specs set by engineer. If you do manual D or have airflow specs would you not think that balancing is part of start-up?

  20. #20
    Join Date
    Mar 2007
    Location
    Okieville
    Posts
    311
    Post Likes
    I dont think he meant that in a racisist way....its just that the people he mentioned NEVER want to spend money....they always just want a "band-aid" to get them by and STILL complain about the price and try to haggle you down or say"well i have a brother thats a handy man and he NEVER charges that much for what your wanting to do. I feel where hes commin from. And if you work on a Performance pay-scale like i do, then you just gotta know when it just needs to be an in-and-out call so you can get on to one that makes money ( in a non-racist way) just the way it has always been in my experiences anyways.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •