Results 1 to 13 of 30
Thread: weak transformer?
05-16-2007, 10:11 PM #1
- May 2007
- San Francisco
- 258
weak transformer?
it's a small water source heat pump. it worked great for years with the mercury bulb tstat. I upgraded to the digital programmable today, but whenever the compressor contactor is energized, I get a voltage sag, the display drops for a second, and I lose the call for cooling. Compressor is only on for a second.
found the primary tap of the control transformer on the factory setting (230 v) but my mains are 208. switched that. same problem, only stays on maybe a second longer.
when 'jumped out' at stat location unit works fine, and in the control box as well.
no unexpectedly high resistance through my control circuits (but I would expect the transformer to overcurrent and fail if I did anyways)
I'm suspecting that years of running at the wrong voltage (and hence higher currents then rated for) have caused this transformer to 'weaken' and it can't handle the inrush current of energizing the compressor contactor coil. Does this line up with anybody's experience?
05-16-2007, 10:32 PM #2
Professional Member*
- Aug 2006
- Vancouver , Canada
- 291
Weak Transformer
I have seen a small transformer ' weaken ' on a bunch of old York Sunline units several years ago when hooked up to the wrong tap, and cause havoc on digital stats.
Check your va ( volt / amp ) rating of the present transformer and ensure you are not drawing excessive current for some other reason. A 40 va transformer should not draw more than about 1.5 amps on the control side.
Easy enough to hook up a auxilliary transformer and see what happens - also, what does the voltage drop to upon startup of the compressor? Is there a bad connection somewhere that is letting the voltage drop below 190 or so on initial inrush?
Keep us posted.Superheat and subcooling tell it all !
05-17-2007, 12:14 AM #3
- Dec 2005
- Spokane Wa
- 169
If it works by jumping from stat and unit, sounds like a problem with the stat. It sounds like the problem arrived when stat was put in circuit
05-17-2007, 12:44 AM #4
- May 2007
- San Francisco
- 258
thanks.
actually (and sorry I didn't mention this), I ruled out the stat as the problem by trying other stats (I keep several in truck stock) and had identical problem with all of them. I think it's either the transformer or a damaged common wire. I have other conductors available so will rule that possibility out tomorrow before changing the transformer.
I'll measure my volt drop at compressor startup as well to see what's going on there.
05-17-2007, 12:49 AM #5
- Dec 2005
- Spokane Wa
- 169
Check for a faulty contactor coil, I have had that happen before.
05-17-2007, 12:54 AM #6
- May 2007
- San Francisco
- 258
would that not cause the transformer to simply overcurrent and fail, if it was a faulty contactor coil? I'll test it as well though. thanks
05-17-2007, 04:22 AM #7
- Dec 2003
- Northern VA
- 619
Any kind of problem with the contactor mechanism such as binding or a foreign object in the plunger mechanism can cause a high amp draw that will not always be fatal to the LV transformer.
I think if the new t-stat was the cause there would be a slight ala Barbecue odor waft in the bargain.
Maybe something got into the contactor when you removed a panel."Iron sharpeneth iron..."
05-17-2007, 08:26 AM #8
make certian that your common is really common at the xformer. if the stat is acting as "power robbing" it could be the issue.
mike
05-17-2007, 09:25 AM #9
- Aug 2006
- 291
Transformer / stat woes
I was in a rush last night when I posted my reply but should add a couple of points -
- when I say the transformers were weakened, I actually measured a difference in the winding resistance on both primary and secondary sides compared to a '' good '' identical transformer, and upon closer inspection under the winding wrap, discoloration was present - they still put out over 23 volts when wired up to line however. I believe the stats the owners were trying to use were Enerstats, which, especially in the early years, had their share of problems.
- the incoming line voltage to this facility was a paltry 198 volts - 3 phase, but other than the transformers not being wired up on commissioning, we had few if any voltage related problems ( ie: compressor or fan motor failures ) except for shortened compressor contact life and control relays burning out.
- the other posts to this thread have been right on!Superheat and subcooling tell it all !
05-17-2007, 09:51 AM #10
- Oct 2002
- North central Massachusetts
- 793
I've had found on occasion a weak contactor coil that closed the contacts but had a voltage drop across the contacts. When I visually inspected them after replacing you'd swear they looked ok.
05-17-2007, 12:23 PM #11
Where are you mesuring this 'voltage sag'? If measured at the transformer it sounds like a VA problem. If it good at the transformer, but drops at the thermostat, then it sounds like you are dropping voltage between the two. i.e. a wiring problem or bad connection somewhere.
I assume you have common wired in at the thermostat, if not and relying on a trickle from "W" to power stat then that is another problem altogether perhaps.
05-17-2007, 06:03 PM #12
My old partner had a problem trying to use an electronic thermostat with a McQuay Water Source Heat Pump unit that he installed in his apartment years ago. It seems that the McQuay unit uses a DC volt relay board to control the loads and it has compatibilty problems with newer electronic stats. He put back the old Honeywell electro-mechanical stat and all the conflicts went away. I don't know if this info will help you. Good Luck.
05-17-2007, 06:13 PM #13
make sure you have a ....TRUE and read it off subbase 24v.... to the new stat...no feedbacks(old styles R only with Y,G,W other side of TR) you have to have the C side at the digital to run it.with that primary 208V and your tapped for 230V could give you a lower secondary when it draws as your seeing.do you have 24 or better coming out ...final solution get a new 208V/24V and more VA if changed out
"when in doubt...jump it out" http://www.youtube.com/watch?v=aMy-sAHwS4E