    Look for this post ......

    " Installing heatcraft in a true "

    its on this page

  2. #15
    When mfrs do this it is because they have the extra capacity built into the condenser to deliver the liquid to the TXV when it opens due to a high load senerio. With a hunting TXV on a tiny critically charged system you risk flood back to the compressor. Now with that said, you can put a TXV in a critically charged system and get it to cool it just wont be right.

  3. #16
    Join Date
    Aug 2009
    Location
    Maine
    Posts
    2,638
    And the customer says it never ran better.
    Quote Originally Posted by Snapperhead View Post
    Look for this post ......

    " Installing heatcraft in a true "

    its on this page

  4. #17
    Join Date
    Oct 2012
    Location
    Wisconsin
    Posts
    2,696
    Quote Originally Posted by lytning View Post
    And the customer says it never ran better.
    Glad to hear that worked out good.

  5. #18
    Join Date
    Jun 2004
    Posts
    847
    I've converted a lot of true box with expansion valve.