    Confused Old Victory Case

    I'm working on an old Victory 2 door freezer. R-502 system with dual cap tube metering. Repaired a leak, change the drier and evacuated. Charged with HP-81 about 80% of name plate charge. Pressures at 30 and 300 in a 85 to 90 degree kitchen box is struggling to even get to freezing. Any info would help I think a differant gas might work better? Yes the condenser is clean.

  2. #2
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,487
    Why did you use HP-81? That's for ice machines where they want a higher discharge temperature for the harvest cycle.

    I would go with HP-80 (R402A) or possibly R408A for that application.

  3. #3
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    14,628
    What ^^he^^ said.

  4. #4
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,765
    what ^^^they ^^^said.

  5. #5
    Join Date
    Apr 2007
    Location
    Loris SC
    Posts
    208

    Why HP-81

    I used HP-81 because it works so well on R-502 ice maker retro fits, I guess its not what I needed here Thanks for the input

  6. #6
    Join Date
    Aug 2006
    Posts
    442
    R-408-a