    On a 115v compressor is the common terminal neutral? this is a really basic question i understand that.
    okay let me have it
    Jul 2011
    Lehigh Valley, PA
    No. Common should be your 115v hot
    Tallahassee, FL
    Typically no. The external overload is usually line which is typically hooked to common.
    Neutral usually goes to relay/ run capacitor.
    Mar 2013
    Quote Originally Posted by SBKold View Post
    I worked on a del field freezer today and replaced start components that another tech had diagnosed as being bad. replaced them all and energized the unit and compressor would not start. i tested for continuity through the windings and had none through start and common or start and run. but had continuity through run and common. but also did not have 115v on common but had 115v on start terminal. did i miss something?
    Oct 2011
    Chicagoland Area
    If you didn't have continuity, you have open windings. A compressor will run with the hot and neutral reversed.
    Mar 2013
    Quote Originally Posted by 2sac View Post
    okay no matter what that was the case then. thanks 2sac. my boss is always calling me up after the fact and saying "did you do this and that ?" "test this and that?" and i always think i missed something.
    Mar 2013
    ahhh, really good to know man! thanks! because thats what i kinda thought i had done
    Oct 2011
    Chicagoland Area
    You should be able to diagnose a small tin can in a matter of minutes with your meter. It normally takes more time to access the terminals than it does to check it out. A compressor analyzer will allow you to check for locked rotor without start components. I know your green. Don't over analyze the situation. Remember the basics. If you haven't been taught the basics, it's time to learn them.
    Mar 2013
    I was positive i was right about the open start winding, then later ,after i had gotten home my boss called me and made me think i missed all kinds of stuff, but yea a compressor analyzer sounds like a good investment. thanks again, your really helpful.
    Jun 2013
    N. Canada
    Quote Originally Posted by northeastbeast View Post
    Don't waste your money on a "compressor analyser".
    In my opinion, they're used by guys that do not know their basic circuits.
    Oct 2009
    Raleigh, NC
    A compressor analyzer is useful at times when you just want to see if you can start a compressor without the start components or when you have suspect start components. A lot of guys just carry a 3-in-1 with a plug attached to do basically the same thing.
    I have a really old HA-1. I very rarely use it, but when I do I appreciate that I have it.
    Nov 2011
    St. Louis
    Sounds like the diagnosing tech missed it and you caught it. And then talked yourself out of it
    Don't forget to check each tap to ground while you have them there in your hands...
    Dec 2010
    Woodbridge Twp, NJ
    Just a dumb question, but did you check the common terminal or through the overload? If the overload is open, both the run and start will appear open.
    Every customer you take for granted today will be someone else's tomorrow.