Results 1 to 13 of 22
    Aug 2013
    Display Freezer High Super Heat
    Service call for a low temp display freezer. Customer stating not reaching desired set point.
    Found a small leak at High Side flare fitting.
    Added 25oz of R404A.
    Checked the system;
    404a
    Ambient temp 80
    Suction pressure 14
    Liquid line pressure 275
    Super Heat Approx 90
    Sub Cooling 10
    All fans were running and coils clean
    Box pulled to set point (-10 degrees)
    Found a small at High Side flare fitting.
    This is throwing me off... I adjusted the unit using sub cooling. Should I be concerned with the super heat?
    just looking for some input.
    Southold, NY
    What metering device,
    X-Valve or Cap tube?
    Aug 2013
    TXV
    It is a Carrier ULG80BC-5, Three Door Glass Freezer (Bottom Mounted Compressor).
    Southold, NY
    Quote Originally Posted by Tbone39 View Post
    TXV
    Forget SC with a receiver.
    Clear the SG and adjust the SH
    Aug 2012
    willowick ,oh
    is there a cpr valve on it. whats the actual #'s on the txv valve itself.Just want to see what kind of valve you got.
    Aug 2013
    Yes to the CPR Valve - 10PSIG
    Not sure what #'s are for the TXV.
    Aug 2013
    I am not sure if I was clear or not… but the unit is operating normal since I have serviced it (About 4 days ago).
    Jul 2012
    Western KY
    Self contained RI freezer. All the time u took to fiddle and think about it you could have pulled charge evacuated and weighed the exact proper charge in. Not picking but I never guess on charge on RIs when the charge weight is on the data plate. Just saying
    Aug 2013
    Since the unit is working now, do I go back, recover, pressure test, evacuate, and weigh in charge. Or should I just leave it since it is operating properly (for now). I am trying to be proactive.
    Southold, NY
    Compressor manufactures call for 20 – 40*f SH at the compressor to prevent damage.
    Aug 2013
    And of course a 90*f Super Heat is bad... Could contaminates cause a high super heat?
    Jul 2011
    Lehigh Valley, PA
    How can you possibly have 90F superheat? On a working freezer?
    Oct 2011
    Chicagoland Area
    If your customer wants to pay for it, go right ahead. Otherwise hope for the best. As far as the SH, first I'd calibrate your thermometer and gauges because somethings not right. You're telling us you essentially have a 70degree suction line at the pump? That pump won't last long and I'm surprised the unit is cooling like you say it is.